Taco 007e failed

Options
brians12373
brians12373 Member Posts: 1

hello. Ilwas my Taco007e installation done incorrectly which could have contributed to the failure. The manual says to install at the 9oclick position.

IMG_0599.jpeg IMG_0597.png IMG_0598.jpeg

Comments

  • HydronicMike
    HydronicMike Member Posts: 331

    A) Are you sure it failed?
    B) It’s installed in an acceptable manner.

    bjohnhy
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,586

    Could be air bound

    bjohnhy
  • 109A_5
    109A_5 Member Posts: 3,915

    I Believe these are two different things. Your motor or maybe more specifically the motor's shaft is horizontal.

    The 9 o'clock is for best viewing orientation of the Junction box.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    jesmed1
  • hot_rod
    hot_rod Member Posts: 27,351

    there seems to be some issues with the molex plugs failing, check that, and return gor the upgraded version

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • SuperTech
    SuperTech Member Posts: 2,657

    That's the correct way to install a 007e on an Energy Kinetics boiler. I believe they come from the factory in that position. Every EK-1F I have worked on has the circulator installed in an identical location.