40-50k btu boiler?
maitoboika
maitoboika Member Posts: 4
edited February 23 in Radiant Heating
Wondering if anybody has experience installing smaller boilers, or know of any decent ones? The system is about 40,000 BTUs, with 7 panel radiators. I was planning on a Viessmann Vitodens 100w B1HE-85. I’ve been having problems finding a boiler with a smaller btu output.
  • DJS
    DJS Member Posts: 6
    lochinvar whb055 or whb085 depending on what your supply water temperature is. If it's 180 degrees the 55 might be light.
    Ibc sfb99-1 works great too.
    Most boiler these days can set a max output or have ramp delays to allow you to not be super oversized.
    I just put a IBC sfc125-1 in my shop and only need about 35,000 btu's for heating and the rest is for DHW. I set the max heating output for 45%(the heating side is maxed at 99,000). But I'm also only heating the floor temp to 85 degrees.
    kcopp
    mattmia2 Member Posts: 16,357
    The better question is what the minimum load is. Most mod cons can operate at a bit less than their max output without a problem but the higher max output means that the min output will also be higher and that could be a problem on a system with a small zone.
  • kcopp
    kcopp Member Posts: 4,663
    The IBC HC will get you between 13k and 50K
    I have a bunch out there. Very reliable for me.
    hot_rod Member Posts: 27,262
    I have a Lochinvar Knight 55K, 51,00 output. It modulates down to around 8,000 BTU/hr. It has nice control features.
    With panel rads you should not need much above 140- 150°