Indirect on warm start boiler
Robert_H
Robert_H Member Posts: 305
I service a Peerless WBV-03-85 (Oil fired) with an indirect water heater. Sorry I didn't note the brand or size I'm guessing 40 Gal and its new looking. It's still has a warm start only aquastat. which drives me nuts.
I want to present to the owners the benefits of installing a cold start capable aquastat which I can explain clearly. However, Im failing to find enough information on potential saving except somewere I read %20 of monthy fuel cost on a tankless coil system is in domestic hot water cost.
Because they heat most of the year with mini-splits they are really waiting money keeping the boiler warm. I just want to present the waste/savings resonably accurately.
thanks
Robert
  • HydronicMike
    HydronicMike Member Posts: 343
    How is it 'warm start'? If it’s an older triple aquastat you can turn the low limit all the way down or modify the control. If it’s a newer one, you can take care of it in the programming.
    A boiler with an indirect really won’t go 'cold' in the summer, unless it’s shut off.
    mattmia2 Member Posts: 16,762
    how do you figure it won't go cold? my indirect is on a modcon, but unless i'm doing a lot of washing something or doing laundry or dishes or showering it runs about once every 8 hours.
    EdTheHeaterMan Member Posts: 12,171
    edited February 10
    I agree with @mattmia2 about the standby-time savings. I previously had a Buderus indirect tank that was extremely well insulated. When no hot water was being used, the only heat loss was through the tank jacket into the living space under the stairs to the second floor. That area had no outside walls, so the heat stayed inside the house.
    The tank would take more than 18 hours to drop just 10 degrees, which was the thermostat’s differential. That worked out to about four 10-minute oil-burner runs every three days while the house was unoccupied. The boiler itself would cool down to room temperature within five hours or less.
    Running the boiler as a warm-start system would definitely waste fuel that isn’t necessary. There’s no exact way to calculate your savings, since your usage may be very different from the vacation home I’m describing, where the house was often unoccupied for five days at a time in both summer and winter.
    If your home uses a lot of hot water, the savings may be smaller because you won’t see the same standby-loss reduction that I did. That said, the bottom line is simple: any boiler temperature maintained above the boiler room temperature is using fuel unnecessarily, and every bit of reduction helps.
    So one tank will take 8 hours of standby before the boiler needs to restart and that is on a very small water content boiler, My experience was 18 hours of standby time and my boiler was a cast iron oil fired boiler that completely recharged the 10° drop in the tank temperature is about 9 minutes and 46 seconds on average. but your standby time could be different and that depends on the boiler and tank that you have.
    The control on the boiler does not need to be replaced and you don't even need to tell them what you are doing if you don't want to. Just remove 2 wired from the Low Limit side of the control and wire nut them together. Viola! you have a cold start boiler. read this post:
    Robert_H
    EBEBRATT-Ed Member Posts: 20,172
    I have an electric water heater. I can shut it off and go away for a week when I come back it is still warm.
    mattmia2EdTheHeaterMan