Tekmar 508 to 518
Options
bgau
Posts: 1
Tekmar shows the 518 as the replacement for the 508, but I feel like my 6-wire setup won't work with this?
Any insight on how to wire to the new thermostat?
0
Comments
-
The 518 will wire exactly the same as the 508. The only difference is the floor sensor terminals on the 508 say "sensor" 1/2, on the 518 you'll use S1 and Com.
0