RIELLO 40 N900s S/N 12M 855925300021
Jalen_Jalen2006
Jalen_Jalen2006 Member Posts: 78
I am having a hard time finding any information on this commercial burner. I’m pretty confident it’s a conversion burner, having intermittent flame failures after cleaning and service. Did not adjust or change electrodes. Also found a manual online could not verify if it was giving me the correct information for electrode/ flame rod adjustment. Today, I ended up changing electrode and flame rod. Boiler fired consistently I am just looking for a pertinent manual or any info at all on these burners.
    HVACNUT Member Posts: 7,434
    This is the only thing I found with that Riello model number. The manual for the heater says to reference the burner manual for setup. Maybe contact Cantherm Distributors.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,530
    Cleaning of flame rod and setting the proper O2 would be the first repair of burner dropping out ..