Hi Everyone,
noticing a new issue with my WM cg-8 boiler. Reverse return hydronic with fin tube.
The boiler starts and runs just fine yet once the temp hits roughly 155 degrees, the boiler shuts off, flue dampener closes. Even though the Delmar 256 says keep going. And then doesn’t fire again until the temp drops to around 130.
the tekmar 256 shows “fire” during this shut off time, yet the boiler doesn’t fire.
if I manually power cycle the boiler, I can get the boiler to fire.
I’’m assuming there is some safely switch that may be tripping once 155 ish is being hit?
The high limit on the boiler itself is 180.
Pressure is good.
thanks for any help,
Have you had a plumber come out and look at it, does it ever turn back on or does it stay off until you power cycle?
If it turns back on but it's reaching temp your temperature probe could be reading incorrectly, need to test the OHMS and compare it to Weil-Mclains chart to see what temp it thinks the boiler is at. If thats reading correctly could also be a problem with the board
thanks @tcassano87 .Tech hopefully coming out today. It does fire up without the power cycle but the temp drops before this can happen.
What are the boilers aquastat settings? It could be they are set low and turning off even though the tekmar is calling.
Thanks @hot_rod. Just a high limit on this one which is set to 180. (510-312-250).
The Relay buzzes a bit, too.
@HVACNUT ! Thank you!
I jumped the high limit and it fired right up.I rotated the high limit dial a few times to maybe dislodge some bits. Testing now.
Maybe best to grab a replacement?Thank you!
I replaced the high limit yet still having the issue.
I'm now down to possible a flow issue??
The supply is about 20 degrees higher than the return (I'm just using a digital infared temp device).
The tekmar has a target of 173 and the boiler shuts off at 162 or so, yet the tekmar shows that it is still firing.
The boiler only starts back up again when the 30 degree differential from the high limit is met.
The limit is set to 180.
The temp/pressure gauge on the boiler corresponds within a few degrees to the tekmar pipe sensor.
Heat is being delivered to all of the heat emitters although the return of each is cooler.
If I jump the high limit, the boiler fire up when the tekmar is tellijng it to fire, yet I haven't tried to crank the high limit and see if the tekmar shuts the boiler off at the target temp.
Thanks for any help everyone!
Thanks @tcassano87 ad @HVACNUT.
I did not out any paste on the probe. Which pase would you recommend, @tcassano87 ?
Trying a probe thermometer soon.
yeah like hot rod said there are a few different types. Honeywell, white Rodgers makes them. They come in single use or like a tub. Might not solve the issue but those aquastats are inaccurate and that could be an inexpensive way to help the situation