3 story building, 9 radiators total on 2 mains, one pipe steam. All radiators on the west main failed to heat all at once, rads on the east main are fine. The west main has a relatively new Big Mouth Vent. Do the Big Mouths ever fail in the closed position? Thanks for your experiences.
Comments
-
easy enough to remove them and see if you can blow through them. it isn't the more likely failure mode but it is possible. much more likely condensate trapped somewhere or water being thrown out of the boiler.
0 -
If you look at how it is constructed with a bellows as a expansion device, if it is operated in the proper orientation, It is highly unlikely to fail to open. Also, If you do not allow it to cool down sufficiently during the heating cycle, it will not open. There is a video on Youtube ["big mouth Update" 2016] covering its construction.
1 -
Just look in the exhaust port the valve it easily seen.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
-
-
Yes, Bellows type vents will not close if they are punctured or loose their ability to contain the gas or liquid within them.
0 -
Just a quick update on the Big Mouth vent that was acting like it was stuck closed.
It happened on a very cold day when the boiler was running frequently. All radiators heated fine on the first cycle, but the Big Mouth stayed closed between boiler cycles and never opened again because of the retained heat. All that brass in a warm boiler room kept the vent closed.
In the video referenced above at 2:15, Peter says the disc remained closed after the steam was released and even after the vent was removed from the rack.
Dennis0 -
Yes, I mentioned this in my January 13 post. The heat in your mains pipe will contribute to this. The ambient temperature in the boiler room is not much of a factor. I assume you are using a thermostat to control your boiler. This happens with thermostat controlled systems and some of the heat timer settings in the cold winter months.
0 -
What you described is exactly what happened. I ended up moving the vent further away from the main.
If that doesn't fix the problem, I will add a different style of vent, either a Gorton or a Hoffman 75. Any difference in the opening/closing temperatures between a Gorton #2 and the Hoffman 75?
Dennis0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 121 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 115 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.8K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements