Pressuretrol acting up?
Removed this ptrol today on a friend's boiler to clean the pigtail. Noticed the pressure was set just over 3psi so we lowered it to 2psi (1 differential).
Now the thing keeps short cycling at 0.5psi. We tried raising the pressure back to 3, still no change.
Ideas?
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
Comments
-
Did you verify the pressuretrol is actually opening on pressure. Like 24 VAC across the pressuretrol's microswitch when the burner shuts down.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
We disconnected the thermostat and the boiler is staying on.. looks like that is the problem
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
OK . . . That may be a problem, but it sounds like a totally different problem. One is shutting the boiler down the other is the boiler is not shutting down when it should.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Yeah. His system needs a lot of tuning. Bad traps and vent, poorly pitched rads etc.
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
(message ment for another thread)
0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 168 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements