Viessmann Vitoden with HTP indirect wiring
Have a Viesmann Vitoden 100-w B1HE-150 tied into a HTPSuperstor Ultra Max MSSU-60N the thermostat tank mount Camco WH9 doesn't talk to the Viessmann boiler tank sensor contacts, boiler is piped with seperate feeds to indirect, no possible using a taco box or will lose temp sensor capability, is there an added relay to fix this. Called Heat Transfer no help
Comments
-
You can either use the viessmann sensor to run your DHW (most tanks have a sensor well of some kind) or any on/off aquastat switch. the boiler comes out of the box ready for the sensor, with the indirect attached to the boilers dedicated DHW taps. If you are piped with the water heater attached directly to the boiler and just want to use an on/off aquastat control (not viessmann sensor) you need to tell the boiler thats what you are doing via the commissioning assistants on screen prompts. The potential downsides to using a switch instead of sensor are that you won't have access to the DHW temps via the VIcare app, and the boiler will run at max temperature during a DHW call instead of based on demand since the sensor can react to temperature changes as needed. You do not need any 3rd party device (not including the aquastat which you already have) to do any of this. The terminals for DHW are the same whether you use a sensor or a switch, but you need to tell the boiler which you are using, and if you don't have the water heater piped to the boilers dedicated DHW taps you will also need to make that programming change ("upstream" is when the tank is connected directly to the DHW taps on the boiler, "downstream" will not operate the internal 3-way valve and instead the DHW call uses the same flow path as the space heating call)
2 -
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements