What type of vent for one pipe baseboard radiator?
In my bathroom there is a short one pipe baseboard radiator with what appears to be a hygroscopic coin vent. There is not enough room to install a traditional vent. Is this the proper way to vent this radiator?
Comments
-
depends on what type of boiler you have. When you say "one pipe" are you referring to steam? If yes, then a hydroscopic coin air vent is not the best however the specifications do allow for venting air from a steam radiator. I'm not a fan of that vent for steam.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
they are marketed as for steam but they are not. you need to figure out how to connect a radiator vent to it, probably need to shift the vent connection around with some fittings and nipples, might need to extend it out of the baseboard cover, can use a straight or angle vent, whichever fits best.
0 -
if it is a hot water system, hydroscopic vents are a good option.
This one has 3 operating conditions, manual, automatic, or off.
If they are used a lot as automatic vents, the cellulose upper cartridge should be replaced every. 2-3 years
This model has a ball check built in, so the upper part can be removed, replaced without relieving pressure in the system.Hydroscopic vents tend to work well with dirty rusty systems . But particles can cause problems.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
1/8” brass nipples and elbows.
0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements