What type of vent for one pipe baseboard radiator?
pjoy
pjoy Member Posts: 3
In my bathroom there is a short one pipe baseboard radiator with what appears to be a hygroscopic coin vent. There is not enough room to install a traditional vent. Is this the proper way to vent this radiator?
    EdTheHeaterMan Member Posts: 12,132
    edited December 2025
    depends on what type of boiler you have. When you say "one pipe" are you referring to steam? If yes, then a hydroscopic coin air vent is not the best however the specifications do allow for venting air from a steam radiator. I'm not a fan of that vent for steam.
    mattmia2bburdpjoy
    mattmia2 Member Posts: 16,693
    they are marketed as for steam but they are not. you need to figure out how to connect a radiator vent to it, probably need to shift the vent connection around with some fittings and nipples, might need to extend it out of the baseboard cover, can use a straight or angle vent, whichever fits best.
    pjoy
    hot_rod Member Posts: 27,416
    if it is a hot water system, hydroscopic vents are a good option.
    This one has 3 operating conditions, manual, automatic, or off.
    If they are used a lot as automatic vents, the cellulose upper cartridge should be replaced every. 2-3 years
    This model has a ball check built in, so the upper part can be removed, replaced without relieving pressure in the system.Hydroscopic vents tend to work well with dirty rusty systems . But particles can cause problems.
  • Waher
    Waher Member Posts: 372
    1/8” brass nipples and elbows.
    pjoy