New build radiant infloor 3 out of 5 loops not getting flow
The system i piped today on a new house when bleeding out the infloor loops I could only get flow out of 2 loops the other 3 had no flow. I removed the pexs from the manifold to check if the manifolds valves were opening that was fine I then tried to blow air through the loops to see if they got crossed and got nothing through on any of them I suspect the got cut during the construction process and possibly blocked by concrete. Is there any way to confirm this or figure out where it might be in the floor so the floor can be removed and a repair done?
    hot_rod Member Posts: 27,065
    Cut, or kinked is more likely.
    You removed all the ends that did not flow, checked them with air pressure?
  • Snowman56
    Snowman56 Member Posts: 6
    Yes I removed the ones with no flow and tried pushing air through and got no flow that way either it just pushed back at me
    frozen?
    rick in Alaska
    with power off you screw the brass ring until the dot lines up with the arrow
    when powered up, thermostat calling, indicator goes to “valve open” position
    Instructions are printed on cover
    The one on the tight is certainly done
    Uponor has an upgrade actuator and adapter
  • Snowman56
    It shouldn't be frozen didn't have any water in til I discovered the problem I filled it tried to bleed air out the the individual loops and got no flow out of 3 of them
    did you put the loops in? Observe the pour?
    I have seen anchor bolts drilled right across a pex tube. That stops flow.
    Kinks where the loops exit the pour is another possibility if they were not sleeved?
  • Snowman56
    I put the loops in. It is sleeved coming out of the floor but I did not personally observe the pour
  • rick in Alaska
    rick in Alaska Member Posts: 1,522
    Just to be sure. When you tried blowing through them, did you have the other end opened, for sure? If you did it one at a time , and only took off the line you are using, maybe something is crossed. In the bad situation you are in, I would take every line off and use air on each one to make sure both ends are open. I have a hard time believing you had that many loops get that compromised.
    Rick
    Grallerthot_rodHomerJSmithAlan (California Radiant) Forbes