c wire
DaveM
DaveM Member Posts: 77
i have an old lennox t90k110c110 thermostat for cool only. the air handler i believe does not have a control board (i will check today)
my question is can i replace this with a new ecobee smart thermostat
    EdTheHeaterMan Member Posts: 11,750
    edited December 2025
    YES
    You may want to add a new thermostat wire if you don't already have an extra unused wire in the wall.
  • DaveM
    thanks Ed i'm going to run 18/5 down to the air handler this is a picture of the transformer down at the unit. where would the c wire connect to thanks again for your help
    mattmia2 Member Posts: 15,992
    what is the label on the lower left terminal?
    is that blue wire connected to anything?
  • DaveM
    the blue wire connects to red wire out of picture going to contactor on outside unit
    EBEBRATT-Ed Member Posts: 19,881
    C is next to R
    You can tell because G & C go to the fan coil relay to start the fan. Move the wires and you will see it is marked C
    oh, because those are the terminals of the actual xfmr.
  • DaveM
    thanks that makes sense ill check tomorrow
  • DaveM
    you are right have 24v between R & C
  • DaveM
    you are right thats the C terminal i have 24v between R &C