THRUSH NO 15E ?? Label partially missing

How does this work? Mainly my question is there is no isolation going to this tank , Supply is feed directly into it on one side and feeds 3 other lines coming out of the opposite side.. I'm replacing the boiler and keeping the system as is because they have no issues with the system ( fintube upstairs and radiant in the lower level) any advice would be great, thank you
Comments
-
-
I wasn't planning on changing anything but the boiler. Like how so? i was going to just power purge with city pressure. There's a return bleeder hose bib by the boiler. They had to have bleed the air somehow with the current design
0 -
@mattmia2 Also conventional to me is 1 pipe in lol
0 -
-
-
-
@mattmia2 That's Exactly how this one is, Supply from boiler goes into the tank and out of the tank on the opposite side..
0 -
water doesn’t actually flow through the tank, it accepts the additional volume increases the water is heated
So water goes in and out with temperature changes. This is possible with a single connection, like the B&G example above
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0