Adding a radiant manifold to existing single zone loop

Options
chippy2
chippy2 Member Posts: 16

ok just trying to think this through ahead of time. I have read books and articles on this but theory and practice are not the same

Existing system is 1 zone fin tube with condensing boiler see pics attached

I already had to remove half the old loop for renovation reasons and would like to add a 4 zone manifold with underfloor PEX

Trying to understand the controls for the circulators and thermostats.

Questions:

  1. does primary loop need to be a specific length vs the circ pump
  2. In my “to be” pic does C3 need to run continuously?
  3. How to determine pump size for each circuit?
IMG_4295.jpeg IMG_4296.jpeg

all feedback appreciated

Comments

  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,664
    edited September 2025

    What kind of boiler do you have? Atmospheric? Condensing?

    If your house is under 4,000 square feet, a Taco 007 or Grundfos 15-42 should work.

    0-10.jpg
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • chippy2
    chippy2 Member Posts: 16
    image.jpeg

    condensing boiler

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,755
    edited September 2025

    Not a condensing boiler.

    Look at the vent pipe. A condensing boiler would use a plastic vent pipe because all the flue gas condensation would rot the galvanized vent connector away in a year. According to the manual this is a better way to do the near boiler piping if you want less problems with air in the system.

    Screenshot 2025-09-24 at 6.13.08 PM.png

    Assuming that you are connecting to standard Baseboard heating units with 3/4" copper tube. The circulator on the return indicates the installer didn't read the manual and followed the directions his father who taught him to do it that way.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Alan (California Radiant) ForbesMad Dog_2
  • hot_rod
    hot_rod Member Posts: 27,080

    here are a couple ideas and a link to an article explaining them.

    IMG_1084.png

    https://www.pmmag.com/articles/84495-a-little-floor-warming-please-john-siegenthaler

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,755
    edited September 2025

    Now adding a radiant floor zone to your existing system will require draining water from the boiler (so you may want to upgrade your near boiler piping at this time) and connecting the zone this way. This is the bare minimum that will work.

    Screenshot 2025-09-24 at 6.13.08 PM.jpg A.jpg

    The controls will need to be added so when thermostat that operated C2 calls for heat , C1 will not operate but the burner will operate. depending on what is currently controlling the boiler, that can be done with a ZC or ZR terminal and a Taco SR501 or equal. Or a Taco SR 503 or equal.

    I can draw you the wiring diagram if you want me to.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • chippy2
    chippy2 Member Posts: 16

    ed. Thanks for this info. A wiring diagram would definitely help me Thanks

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,755
    edited September 2025
    Screenshot 2025-09-28 at 11.11.24 AM.png

    Any Questions?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Alan (California Radiant) Forbeschippy2
  • chippy2
    chippy2 Member Posts: 16

    two questions:

    1. In the layout you provide above showing the secondary circuit shouldn’t they need closely spaced T’s?
    2. Does the mixing valve still protect the boiler in this case or is it simply reducing radiant floor circuit temperature?
  • chippy2
    chippy2 Member Posts: 16

    Yes sorry that was a typo. Should be read NON condensing boiler.


    also the Kitchen circuit in the lower right corner was removed and capped at both ends during renovations

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,755

    chippy2 Member Posts: 6

    7:44AM

    two questions:

    Q: 1. In the layout you provide above showing the secondary circuit shouldn’t they need closely spaced T’s?

    A: This is a layout that will work without too much repiping. just adding a zone that is connected to the supply and the return. if you are going to get more involved with a piping redesign

    Q: 2. Does the mixing valve still protect the boiler in this case or is it simply reducing radiant floor circuit temperature?

    A: No that layout does not have boiler protection. That layout is "The Minimum" you must do. I think @hot_rod Bob's post has some better layouts. too bad they are a little out of focus but the link is still good.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,755
    edited October 2025
    Screenshot 2025-10-05 at 11.06.45 AM.png

    Since you have baseboard hot water radiators, there is not much water volume in your system. For that reason you never actually needed boiler temperature protection. The return water heated up quickly. By adding a low temperature radiant heat zone, then you will be returning much colder water if only that zone is operating. So this is a redesign that I might use. In your "proposed" drawing the radiant heat zone circulator will not get any hot water from the boiler unless the boiler C3 is operating to move heated water past the closely spaced tees. Whenever C3 is operating there will be a tendency for the baseboard loop to get some ghost flow or thermocycling or even forced flow even though C1 is not operating. that is because the baseboard loop is not connected to the primary boiler loop

    I didn't see your proposed diagram when I first looked at your post. That is why I offered the "Minimum Diagram". Now that I can see that you are using three circulator pumps, I will offer you this diagram with four major corrections.

    1. I have pasted the near boiler piping from the I/O manual from Pensotti.
    2. I have corrected the closely spaced tees. The idea is to have next to zero pressure drop between the supply to and the return from the secondary loop. By putting one of the Tee fittings on the corner of a run in the primary loop, you are creating a pressure difference between the supply to and the return from a secondary loop.
    3. I have placed the hotter secondary loop first on the primary loop. The second lower temperature secondary loop will be able to operate with lower temperature water from the first secondary loop’s return. Since both primary and secondary can operate at the same time and also only one at a time, the water temperature feeding the low temperature secondary loop will be different if the high temperature loop is operating or is not operating. Since this happens without notice, the manual mixing valve idea will not work so that brings me to fix #4
    4. Install an automatic mixing valve.  

    I hope you find this helpful

    Mr. ED

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    chippy2
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,755

    I would purchase a Taco SR 502 (or 503) to operate the zone one and the zone 2 circulators separately using separate thermostats. Here is that diagram

    Screenshot 2025-09-28 at 11.11.24 AM.png

    Any Questions?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    SteveSan
  • chippy2
    chippy2 Member Posts: 16

    Ed thank you. I don’t see you updated diagram that you are describing 🙁 I do see the control circuit however

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,755

    Oops… I edited my previous post with the diagram.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Member Posts: 27,080

    if the radiant us around 10% of the boiler btu output , I would not be concerned about return protection

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • chippy2
    chippy2 Member Posts: 16

    the radiant floor circuits will cover about the same square footage of floor space as the existing, remaining sq footage of floor space that the baseboards are heating

    Using aluminum trax under floors 1/2” PEX


    was looking at the Caleffi mixing station W three zones and the Taco 503

  • chippy2
    chippy2 Member Posts: 16

    Ed sorry to bother. Maybe I’m not seeing it but, I still don't see a diagram you updated ( even when I follow your latest link?)

    What / how am I missing it?

    Can you repost it one more time? Thank you!

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,755
    Screenshot 2025-10-05 at 11.06.45 AM.png

    I don't know why it is not coming up on my edit. Here is it in a new comment

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • chippy2
    chippy2 Member Posts: 16

    got it thanks!