Webster Type R System in my 1934 colonial
System works well just showing it off. Very unmolested system. Currently being steamed up by a 1998 Burnham PV73ST-HBUR. Output is 379 sqft of steam.
Has the original radiator valves by Webster, original Webster radiator traps and American Radiator Corto radiators. Thinking of upgrading to a vapor stat to hopefully save on some fuel may need to talk to a plumber friend of mine to see if that is a worthy upgrade. Also considering doing some maintenance such as fresh cage units for the traps. I also do need to put a new chamber in the boiler it is in pretty poor condition I'll probably have my plumber friend give me a hand with that as well. Other than regular maintenance/cleaning and the occasional new part such as low water cut off/primary control/motor for the burner it's been a fairly reliable burner/boiler
Agree
Since we are getting closer to heating season here in Connecticut doing the cage units will probably wait until next summer but when I have the week off in between Christmas and New Year's I'll take care of doing the combustion chamber, filters, nozzle and cleaning the boiler
Does the boiler cycle? how does the boiler size compare to the connected radiation? the vaporstat will only do something if the boiler is too big. if the pressure is controlled the traps shouldn't be doing anything anyhow.
It doesn't cycle. It just runs until the thermostat is satisfied. Boiler is also my domestic hot water so not sure if that has anything to do with the cycling or not. I'll have to find my pad but I did figure out the EDR of all of my radiators and it's very close.
@WilliamGwiazdowski , that boiler is at least 35 years old. Make sure it's not leaking before you put much money into it.
Where are you located?
Consulting0 -
@Steamhead Southeast Connecticut. It was installed in October of '98 and the rating tag says it was manufactured in June of '98. Trying to keep it going as long as possible. As far as I can tell it's not leaking. I do regular checks of the gauge glass and it barely moves and I barely have to add water to it. There's no auto feeder on it.
flood it, turn it off and fill it up to the steam riser, let it sit a couple hours and see if water comes out anywhere. that will test for leaks above the water line
you could add a 0-3 or 0-5 psig gauge to it and that will let you know if it is actually building any pressure now. sometimes the low pressure gauges available are calibrated in oz/in^2
Good suggestion. I have before opened up the pressure relief when it's steaming and I do hear a little pressure come out.
38 years is a good run from any boiler especially a Burnham. You could make it to 50 years.
If the boiler runs without shutting off on a call for heat until the stat is satisfied don't waste money on a vaporstat.
" It was installed in October of '98 and the rating tag says it was manufactured in June of '98. "
I get one month short of 27 Years of service. Or only a few months over 27 Years old since it was made.
If you like the gauge idea and your EDR is well matched to the boiler you may want something like this, a Dwyer Magnahelic Gage, Not too expensive on eBay. Many variations to choose from. You could build a water Manometer with clear tubing to get into the correct ballpark.
My boiler (slightly undersized) never goes over 2 inches of water column. 1PSIG = 27.679 inches of water. Even on a 3 PSI Gauge 0.072 PSIG would be hard to see.
BTW if your pressure is as low as I expect a Vaporstat may be a waste of money, since it will probably never trip. I think I'd figure out what your pressure actually is first.
One Pipe System0 -
It has served us very well. No real issues other than a new low water cut off as well as normal maintenance to the burner and normal cleaning of the boiler. I did have a mystery water leak last year but I figured it out the drain valve was leaking so I simply capped it off with a garden hose cap.
- 117 Geothermal
