hello techs , recently worked on boiler had to pipe in relieve valve to bldg drain, found PRV leaking causing system to lose pressure, the location of the prv is tight no space to work , I want to relocate the new prv & back flow preventer so it accessible for future repalcments ,i.ll share job pics any suggestions would be great,

1000046298.jpg 1000046292.jpg

as the job looks simple.

Comments

  • hot_rod
    hot_rod Member Posts: 25,510

    Sure, a combo package makes that easy.

    Replace that pressure relief also.

    Is that a LWC with no wires connected? :)

    Screenshot 2025-08-26 at 11.52.13 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,879
    edited August 26

    I like the combo units also.  They come with a union fitting so you don't need to cut pipes to replace the parts in the future. If you pipe it near the expansion tank and include an isolation valve on both sides of the setup, you can service the expansion tank, back flow preventer and auto feed PRV without draining the boiler or shutting off the house’s potable water supply. This Expansion Tank Fitting on one end and that ball valve on the other end will accomplish this nicely.

    Screenshot 2025-08-26 at 4.06.48 PM.png

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Member Posts: 25,510

    Looks like you are pumping into the boiler? Air purger and expansion on the supply side of the boiler?

    An upgrade would be to connect a tee above that pump, tie the tank and fill valve there.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,879

    If I repiped this one it might look like this

    Screenshot 2025-08-26 at 4.45.28 PM.png

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Member Posts: 25,510

    Or this option.

    Above the pump, below the yellow ball valve is a coupling. Remove that, install a tee with 1/2 branch. Tank and fill connect there.

    Screenshot 2025-08-26 at 3.07.07 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • HVACNUT
    HVACNUT Member Posts: 6,955

    Are we going to address the discharge piping on the relief valve?

  • mattmia2
    mattmia2 Member Posts: 13,872

    I had plans to do something other than addressing all of the issues in those pictures tonight. It would be easier to cut everything back to where it comes out of the house and the boiler and start over than to try to fix what is there.

  • nytech28
    nytech28 Member Posts: 99

    yes its pumping into the boiler, air purger & expansion on supply side. i.ll visit the job again & evaluate the upgrade to owner boiler poorly maintained over the years ,thank you for your time.

  • nytech28
    nytech28 Member Posts: 99

    I replaced the pressure relieve valve & tead boiler 1 & 2 relieve valve into floor draine ,LWC is not even connected ,I initially came in May to help stop relieve valve leaking water on boiler 1 & left job for September due to hvac season, looks like ex-tank full of water i cant even press the air pen to test it , poor maintenance & safetys bypassed by unprofessionals just to make few bucks & runaway ,am going to fix all issues i.ll share pics of the piping on the releive valve .thank you for looking in.

    1000046369.jpg 1000054870.jpg 1000054869.jpg 1000054868.jpg
  • hot_rod
    hot_rod Member Posts: 25,510

    well, we have seen worse🧐

    What type of heat emitters?

    I’d wonder about the dirt or corrosion particles on top if the jacket. How does the burner tray look?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • nytech28
    nytech28 Member Posts: 99

    baseboard heat, boiler needs complete cleaning to make it simple.

  • nytech28
    nytech28 Member Posts: 99

    thanks for drawing it out for me ,it make things much easier, as I am hvac guy that works on air conditioning, most of the time.

  • nytech28
    nytech28 Member Posts: 99

    I aprecaite taking the time to draw this out for me ,makes job go much easier & practicle.

  • nytech28
    nytech28 Member Posts: 99

    so am pumping away from the ex.tank , in this setup

    EdTheHeaterMan
  • hot_rod
    hot_rod Member Posts: 25,510

    To check the expansion tank, push in the tire stem "needle" or sometimes shake or rattle the tank to see if it is water logged.

    Often on neglected systems it is best to price all the safeties or "consumables"

    Fill and BFD, relief, LWC, expansion tank. The cost of these items is probably much cheaper that repeated call backs to find yet another failed component.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • nytech28
    nytech28 Member Posts: 99

    Tire stem would not move looks like its water logged , owner already gave me the green light to repair the boiler so price shouldn't be issue ,thanks again

  • hot_rod
    hot_rod Member Posts: 25,510

    sounds like you are trying to do right by the owner. Keep checking in. Someone usually has an answer

    Or @EdTheHeaterMan will make something up🤓

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • nytech28
    nytech28 Member Posts: 99

    man you guys are great ,very knowledgeable & helpfull , GOD BLESS

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,879

    "so price shouldn't be issue"

    Famous Last Words!

    I will suggest that you price all the components @hot_rod suggested, including the labor to install them as a single flat rate for the complete job. It will come to a high price that you will propose to the owner. Then you can do an individual price for each component separately. those will al be lower of course but when you add up the individual prices the total will be much higher when completed separately. This approach will usually get the entire job completed up front, with the approval of the customer knowing what the price is going to be up front. Then you don't have a problem collecting after you are done because "I didn't think it was going to be that much" after the job is completed. Then you get to spend more time that you don't get to add to the bill in order to reduce the bill for what is already completed.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,879
    edited August 27

    I looked at the After Photo and might make this observation. Your solution might be in violation ANSI Z21.22, and I'm sure you did not intend to do that.

    In Accordance with ANSI Z21.22 No valve is to be placed between the safety relief valve and the tank. A discharge line shall be connected to the outlet of the valve and shall pitch downward from the valve. Discharge line shall terminate through plain (unthreaded) pipe with at least a 6” (152mm) air gap from building drain or other approved location where any discharge will be clearly visible. In no case may a discharge line be directly connected to a sewer line. No reducing coupling or other restriction shall be installed in the discharge line. The discharge line shall be installed to allow complete drainage of both the valve and the line. Discharge line material must conform to local plumbing codes or ASME requirements. Excessive length over 30’ (9.14m), use of more than four elbows, or reducing discharge line size will cause a restriction and reduce the discharge capacity of the valve

    You can find this information on just about every relief valve tag that is supposed to be left in place after the valve is installed. Here is a typical tag:

    Screenshot 2025-08-27 at 10.27.58 AM.png

    This photo represents a situation where the discharge is not visible with a minimum of 6" air gap and where it is directly connected to a sewer drain pipe.

    Screenshot 2025-08-27 at 10.38.48 AM.png

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Member Posts: 13,872

    I also wonder why there was a trap in that drain and there isn't one now.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,879

    Washing machine discharge?!? maybe

    I might suggest this design. include all the relief valves for each boiler and water heater. Try not to use more than four 90° elbows.

    Screenshot 2025-08-27 at 10.38.48 AM.png

    A trap on the drain line may also be necessary.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • nytech28
    nytech28 Member Posts: 99

    I would say yes i do agree on the pricing formullah you provided was good. checking the job after its done does take up time.

  • nytech28
    nytech28 Member Posts: 99

    there was a washing machine in past not sure if photo can show there's still hot & cold water lines which are not used.

  • mattmia2
    mattmia2 Member Posts: 13,872

    If that drain goes to a sewer it needs a trap.

  • nytech28
    nytech28 Member Posts: 99

    yes indeed i did not intend piping to sewer line to do fast job ,that's why am sharing the job photos,to execute the job professionally & upto code i.ll have to correct the relief piping , I do have the 2 boiler relieve valves tead together which I would have to redue.

  • hot_rod
    hot_rod Member Posts: 25,510

    is it possible the white pvc just sits over a floor drain that is trapped? If so that is an indirect waste, and legal.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2EdTheHeaterMan
  • nytech28
    nytech28 Member Posts: 99

    there is no floor draine in the boiler room ,the pvc travels towards the basement bathroom erea & not sure where it ends ,mostliky bldg drian system .

  • nytech28
    nytech28 Member Posts: 99

    I can add my own trap on the white pvc before the open funnel. as pictured.

    1000055329.png
    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,879

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    nytech28
  • hot_rod
    hot_rod Member Posts: 25,510

    but if there is already a trap on the line, you don’t want a second trap

    Find where that line ends up. If in fact you add a trap, by code and for proper operation it needs to be vented

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    nytech28
  • mattmia2
    mattmia2 Member Posts: 13,872

    (depending on where it goes it might be wet vented)