Air conditioning condensate
I'm curious,
Is there a general rule of thumb of how much condensate an air conditioner can produce per ton per hour?
I understand there's a huge amount of variables, I'm just curious if there's some formulas out there. I.E. if you've got 5 tons of cooling and 12,000 btu/h of that is for latent cooling, what amount of water can that produce?
I'm producing just over 3 gallons per hour of condensate with a 5 ton system and I'm running something like 420 cfm / ton, so sensible is higher than I'd like it.
I took a guess.
25 pounds of water per hour = 24,250 btu/h?
When water condenses, it gives up heat. This is just the latent heat of vaporization.
As stated in the opening question, to figure out the water production in a particular situation requires knowing lots of details. But if you just want a ballpark limiting case, you can use the heat of vaporization to calculate the maximum amount of water it would be possible to condense with a given amount of heat pumping.
will give you the heat of vaporization of water at any selected temperature, say for example the evaporator coil temperature. Take the latent heat pumped / specific heat of vaporization to get water condensed.
EG. the latent heat of vaporization of water at 55F is 1062 BTU/lb. If you are pumping 12000 BTU/hr of latent heat then you are condensing 11.3 pounds per hour of water.
Note that I made the problem easy by assuming a fixed about of latent heat pumping. The actual amount of latent heat removed depends on all of the variables, so by fixing that number I am ignoring all of the complexity. This is foolish if you are trying to figure out how much water will actually condense given particular conditions, but perfect if you just want an idea of the maximum amount of water that could possibly condense if all the cooling went to condensing water.
If you really need to know just pipe the condensate into a 5 gallon pail that is marked off in 1/4 pound increments or in 4 ounce increments. Then set the thermostat in an 80° home to 50° and watch for the water to start pouring out the pipe. Once you get a steady and consistent flow, place the bucket under the discharge pipe in order to collect all the water from the operating air conditioner. start a stop watch at the same time. In 15 minutes remove the 5 gallon pail and measure how much water you have. Now do the math for the number of pounds and ounces of water you have based on the 15 minutes, times 4 to get you the hourly number.
Repeat this on several different days when the RH and Temperatures are different.
Then Repeat with several different homes that have different size AC units.
At the end of the summer, report back here with your findings.
We all would like to know this important information in case we will be installing 20 or more units in the same building and need to know what size common drain pipe is needed for all that water if all units are operating at the same time.
here is an online calculator
the latent heat of vaporization of water will get you there. figure out how many gallons 12,000 btu will evaporate and you have the theoretical maximum. Or convert it to watts and it will al be a lot easier.
Something is seriously wrong with that calculator.
I didn't try it myself. Is it way off?
Yeah,
I did something like 80f 70% rh and 2000 CFM and it came up with 3+ gpm.
For 1200 CFM. 72f and 45% it still said something like 0.5gpm. I have no idea what it's using as the evap temp but it's cold.
- 15.8K Strictly Steam