Chilling me softly with

Options
hot_rod
hot_rod Member Posts: 27,904

his HP. Chilling my whole shop with his HP.

91° outdoor today so I put the VitoCal A2WHP in cooling mode this week. I'll give it overnight to bring the slab ° down.

Screenshot 2025-06-26 at 8.12.40 PM.png Screenshot 2025-06-26 at 8.13.01 PM.png
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
Joannie

Comments

  • mattmia2
    mattmia2 Member Posts: 17,571

    is it dry enough that you won't have a swamp tomorrow?

  • hot_rod
    hot_rod Member Posts: 27,904
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • hot_rod
    hot_rod Member Posts: 27,904
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    EdTheHeaterMan
  • mattmia2
    mattmia2 Member Posts: 17,571

    wasn't she on the first snl?

    EdTheHeaterMan
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,730

    I love the connections. Thanks.

    Retired and loving it.
    EdTheHeaterMan
  • Nick_Castrads
    Nick_Castrads Member Posts: 93

    Really interesting @hot_rod, we're running a similar trial in our showroom in London. We've been keeping the flow temp just above dew point. It has had a modest cooling effect but the ∆T is so small between ambient and water temp that the we're talking a degree or two of cooling effect. We'd need to add condensate drains and chill the water further, and introduce fans to move the air around in order to get more siginificant cooling.

    Would love to hear how you're getting on a month on. Has it had a significant effect? What were the ambient, flow and return temps? What emitters are you using? Is this a radiant floor?

    PC7060
  • mattmia2
    mattmia2 Member Posts: 17,571

    usually they do radiant cooling in large buildings where they duct in ventilation air and that ventilation air is already dehumidified.

    or move to the desert like @hot_rod

    PC7060
  • ChrisJ
    ChrisJ Member Posts: 17,534

    I used to watch a movie as a kid where they show what I thought was supposed to be an alien facility on Mars.

    I found out recently, no, that's not Mars, that's just Utah and that's actually how it looks. Dusty.....dry..

    Very different from anything I've ever known which is usually very hot and humid. Our dew points have been 70-80f lately.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    PC7060