Boiler Header Manifold

tcassano87
tcassano87 Member Posts: 96
IMG_8341.png

Anyone familiar with this brand boiler header manifold? Price is so low it almost worried me a bit. I’ve used legend before and it’s a great product but happen to come across this so figured I’d check to see if anyone has a quality report from experience

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,816

    Probably China. I am sure it is fine if the welder knew how to weld.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,492

    As long as there is not too much Chinesezium in the welding rod used.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    tcassano87EBEBRATT-EdMad Dog_2Alan (California Radiant) Forbes
  • mattmia2
    mattmia2 Member Posts: 12,801

    i'd be more concerned about the pipe and the threads which aren't mutually exclusive

  • tcassano87
    tcassano87 Member Posts: 96

    the welds were actually what I was most concerned about. The pipe has to be up to some kind of standard lol but of course the threads could be no good which then you’re screwed either way

    Alan (California Radiant) Forbes
  • mattmia2
    mattmia2 Member Posts: 12,801

    its not like someone is inspecting the factory to see if it meets those standards

  • hot_rod
    hot_rod Member Posts: 25,112

    From a warehouse in E Brooklyn?

    Screenshot 2025-05-16 at 8.00.30 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • tcassano87
    tcassano87 Member Posts: 96
  • mattmia2
    mattmia2 Member Posts: 12,801

    i assume it is made in china at that price. it looks like it is distributed by one of a number of companies that curtiss-wright acquired over the past 20 years

  • GroundUp
    GroundUp Member Posts: 2,354

    I've used them several times with good results. With that said, be very careful with that company. I used to spend tens of thousands per year there and while they were usually okay, the instances where they'd ship the wrong item or skip something in the order was like pulling teeth to get a resolution. Customer service is beyond horrible and the supervisor is downright insane- always blaming the customers for the company's faults. We're currently involved in a legal battle where they took payment for a several thousand dollar order and never sent it out.

    tcassano87
  • mattmia2
    mattmia2 Member Posts: 12,801

    can't you usually just claim something like that with your credit card company?

  • hot_rod
    hot_rod Member Posts: 25,112
    edited May 17

    Id be surprised if it is even schedule 40?

    i think the original Speedy Header brand were made in the US.
    Earth Lee was another custom made brand

    IMG_0376.jpeg

    Sioux Chief, Alberta T drill and Precision Hydronics have copper headers available

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • tcassano87
    tcassano87 Member Posts: 96

    are you talking about out Pex Universe? Luckily they have a store like 15 minutes from my house if there is any issues

  • tcassano87
    tcassano87 Member Posts: 96

    According to the description its schedule 40

  • mattmia2
    mattmia2 Member Posts: 12,801
    edited May 17

    supplyhouse.com shows 2 different brands, one that is like $40 and one that is like $120. there could be many reasons for the lower price, many of which may have nothing to do with the actual product, but one might be made in china.

  • tcassano87
    tcassano87 Member Posts: 96

    yeah def assume China they were cheap enough I could order them, take a look a see the quality. If they looks no bueno, bring them back no harm

  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,173

    We used BASCO on Long Island in the 1980s & 1990s…Excellent & reasonable. Haven't seen them in years. The biggest issue I've seen with the cheap imports is not the welds, but the branches not being 100% plumb with eachother…skewed....Mad Dog

    mattmia2tcassano87
  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,427
    edited May 17

    Far be it from me to second guess people motives, tendencies and persuasions, but why not install a quality brass manifold with individual shutoff valves, union connections and flow meters (Roth, Rehau, Uponor…..). Will it really break the bank?

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    hot_rod
  • hot_rod
    hot_rod Member Posts: 25,112

    there are certainly good , better, best pricing and products out there.

    For manifolds, cast or forged brass from Italy is tops, stainless or plain copper stubs next level, and no name steel import may be the lowest price.

    Even with a jig metals move when welded or brazed. I struggled with this when making copper T Drill manifolds by hand. Luckily a copper braze leaves you with a “movable” branch😉

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • tcassano87
    tcassano87 Member Posts: 96

    because the feed/return header is being done in Black pipe. Then there will be isolation flanges on both sides of every circulator. The one radiant loop will indeed have a mixing valve & an Uponor radiant manifold, the rest of the house is baseboard

    Alan (California Radiant) Forbes
  • tcassano87
    tcassano87 Member Posts: 96

    so little update, they are def schedule 40, but very inconsistent.
    5 Zone all the welds look good(IMO) 3/4 stub outs were straight but the pipe itself had a bow in it

    The 2&3 Zone was straight but unfortunately the welds did not look great to me.

    So I won’t be using them, doesn’t seem like a bad product, just very inconsistent like many mentioned

    mattmia2
  • pedmec
    pedmec Member Posts: 1,215

    The bow in the pipe is due to heat from welding the nipples. I'm having an issue with my welder installing 1-1/2 threadolets on 4" schedule 40 steel. I'm having them installed with 8" spacing's. He's having me buy schedule 80 to handle the heat and he's going to run water thru it to keep it cool.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,816

    @pedmec

    I have had that issue. They make nice skis when your done. Never tried the water trick.

    Only way I ever found was to heat the 4" to relive the stress. Putting the tapping on opposite sides of the pipe would help balance things out but you can't always do that.

    Instead of using thread-o-lets they make pipe-o-lets which are much lighter and have less mass and don't require as much weld metal so you get less shrinkage

    GroundUp
  • mattmia2
    mattmia2 Member Posts: 12,801

    can you move along the manifold doing about 1/8 of each fitting at a time and still end up with a good weld? i assume you have to tack them square first

  • pedmec
    pedmec Member Posts: 1,215

    @EBEBRATT

    I'm doing the threadolets so I can bush them down to what I need and if I need to increase the pipe size for a particular zone for whatever reason I'm not locked into the small size. I like to keep my options opened. Once its welded, it's welded if you know what I mean.

  • pedmec
    pedmec Member Posts: 1,215
  • hot_rod
    hot_rod Member Posts: 25,112

    the two dimensions that need to be kept in tolerance are the branches square or 90 degrees to the trunk

    Then the axial tolerance , looking down the trunk, from an end, do they all plumb to one other.

    The farther away you pipe from the branch, the more noticeable any variance will be

    We have run into this with hydraulic separators that we weld. If they put long trunks on the outlets, even a tiny out of tolerance on the branch weld position to show

    Warping of the trunk in to an arc is yet another concern, but the easiest to correct

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • pedmec
    pedmec Member Posts: 1,215

    The only other option that I could even remotely think about doing with was mechanical tees and I don't think that is a very professional looking manifold.

    propress and Megapress is not an option not only due to cost but you are not guaranteed a straight piece of pipe either.

    a tee puller we don't have plus time consuming.

    so I have faith in my welders to keep it straight. 🙏

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,816

    Unfortunatly metal shrinks after welding and weld o lets are heavy and take a lot of heat and a lot of passes.

    You can clamp the pipe down and tack the pipe to a strong back and it will still warp. In fact it will just break the tacks.

    Stress releafe with heat is my only trick.

    I know you want to keep your options open on branch pipe size but the larger the weldo let the more warp you get.

  • mattmia2
    mattmia2 Member Posts: 12,801

    Could tig vs mig vs stick make a big difference here? Unless it is steam or there is a spec requiring black if you are doing it for cost copper with the right t drill is probably the least expensive over several installations. Doing it with black fittings and nipples is definitely an art and making that look good is definitely a professional job.

    Not really sure what you're trying to accomplish with this.

  • pedmec
    pedmec Member Posts: 1,215

    Just trying to do a professional job that's all. Customer is paying six figures for a boiler room and I think he wants a six figure professional job in return.

    And I'm not hiding it with insulation lol. The old Weil McLain 1086 supplied all the heat for the basement by just sitting.

  • mattmia2
    mattmia2 Member Posts: 12,801

    US made black fittings would be my first choice if it were mine. Copper would be my second. Leave a capped tee on the end and space to add more zones if needed. A caleffi hydraulic separator makes a nice job for air and dirt separation with hydraulic separation. I'd rather see fittings and zone/isolation/balancing valves and flow meters as separate parts vs an engineered manifold with proprietary parts that might disappear.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,816

    Nobody wants to thread 4"

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,816

    You could use 4" black and put Victaulic mechanical tees on. There like saddle taps. You just hole saw the holes in the pipe and bolt them on. That's the best way to do hot water and cheaper than welding and getting them aligned is easy.

  • mattmia2
    mattmia2 Member Posts: 12,801

    Isn't this hot water with like 1.25" near boiler piping?

  • pedmec
    pedmec Member Posts: 1,215

    @ebebratt-ed I priced it for mechanical tee's but having 7 takeoffs on each manifold with mechanical tee's is kinda going to make it look ridiculous, in my opinion. Having the welder do threadolets is really not going to cost that much more. Mechanical tee's are 5X cost of a threadolets. the rest will be done in grooved. 2 RBI boilers with buffer tank, air separator, etc. the issue is space. The job is in the basement of Cheers (RIP George). absolutely no space. I have a plan

    @mattmia2- its a 4" supply and return. seven story building.

  • pedmec
    pedmec Member Posts: 1,215
  • mattmia2
    mattmia2 Member Posts: 12,801

    you could run some large branches and put the manifolds on remote locations if you can find spaces for that. might ultimately take up a lot less of the basement if everything doesn't have to home run to the boiler.

  • GroundUp
    GroundUp Member Posts: 2,354

    @pedmec perhaps it's time to find a welder that knows what they're doing or send this one to class. Heating or welding a diamond on the opposite side of the pipe will prevent the spring and any actual pipe welder learned that on day one.