Soot in 5 months

I was distressed today to find soot in the pipe and heat exchanger of a boiler I did the annual service for in September 2024. I've been servicing this boiler for 3 years. Today I was replacing the water feed etc (separate post) and I pulled the pipe for better access and found the soot.
Burnham V-14A-T, Calls for a 100-80A and 100 PSI. I have been running a 85-80A at 140 PSI.
This was the final CA in September, Zero smoke -1% CO2 breach draft -.03.
Tstack 647
O2 4.9
CO 11
EFF 79
ExAir 28.5
CO2 12.03
This is CA as found today
Tstack 560
O2 4.5
CO 15
EFF 81
ExAir 25.6
CO2 12.33
Draft in the breach between -.03-.05 OF -.01-.03 (windy)
The pipe had thin coat of soft soot. The HX had between 1/8 and 1/4" of soot laying on the top of the hx visible with the pipe removed and the pins were coated, at least what I could see from the pipe connection. the firebox was soot free. I cleaned the pipe and vacuumed the top of the HX through the pipe hole and will be back to thoroughly clean this weekend, pull smoke, CA etc. the soot sucked up easy as if it was just laying there.
I'm not seeing a big difference in the CA values at least not what I would think would create soot but I'm still learning. Is there anything standing out in these CA values?
And, besides a good cleaning and tuning is there something else I should be looking at.
Thanks
Robert
Comments
-
Sounds like the flame is impinging (touching) something it shouldn't.
What burner is on it? Did the target wall detach from the back of the firebox and tilt toward the front?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting3 -
You are pushing the limit at 12.33 CO2. You have no assurance that this value is steady and it could climb to 13 in certain draft conditions. I would not run it that high………….get down to 10.5 and be happy.
I recently reset a fairly new boiler that was running 13.5. It sooted itself up badly in 18 months. Of course, the individual who set it had no combustion analyzer. He was so good he could set it by eye. Just ask him!
5 -
Agree with @LRCCBJ
Your adjusting the burner too tight.
People don't believe this but things can actually change:
The blower wheel picks up some dirt
The fuel supply is different quality
the temp of the combustion air changes
the temp of the fuel changes
The draft changes based on outdoor air temp
etc etc
There are many variables. You should adjust the burner to 0 smoke where if you closed the air any more it would lead to smoke. Then open the air until the Co2 drops 1%-2% from where it was at 0 smoke.
This leaves a little margin or cushion to work with.
There is no sense trying to get the last bit of efficiency out of a boiler to risk getting soot. The fuel saved is nex to nothing
I wouldn't run anything over 12%, 11.5% is probably better.
4 -
-
Use the method @EBEBRATT-Ed outlined above. I never leave a boiler like that running above 12% CO2. Make sure the combustion chamber is in good condition. What about the ignition components? Are they in good shape? How did the flame retention head look?
It's also a good idea to check combustion during ignition, steady state combustion and and after the burner shuts down. You might find the CO PPMs are excessive during ignition, this might be where the soot is coming from.
1 -
-
All good stuff thank you. So testing during during ignition, during steady state and during shutdown sounds great my question is if I see hi Co during startup what does it mean I'm assuming it means delayed ignition. And what about after shutdown if I see high CO what comes to mind for me would be I've got an after trip that's burning off… sorry for asking amateurist questions but the guy I work for is not a big CA guy. He did buy an analyzer in a smoke tester and I end up buying my own. And yes I do need to take some classes and am working on that.
0 -
This boiler also has cleanout plates under the jacket on the right side.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
If you are measuring high CO after ignition I would start by checking the ignition components. Ohm test the igniter. Make sure the electrodes are properly adjusted and in good condition. I would check the cutoff on the oil pump. The nozzle could be dripping after the burner shuts down, that would cause high CO and smoke during ignition. Was there any oil in the burner chassis or the air tube?
0 -
yes, it does
0 -
-
Combustion testing during the entire burner cycle is something that the NCI recommends. I have found problems this way, things like the nozzle dripping after the burner shuts down.
And I wholeheartedly agree that all burners should have solenoid valve or clean cut oil pump. I also prefer to have a modern primary control setup for interrupted ignition, 10-15 second trial for ignition, pre purge and post purge.
0 -
I would make sure that there is enough make up air to the burner. Some houses are very tight with little air infiltration. Also I agree about CO2. I like to set to 11 to 11.5% in case the cat or dog walks past the burner. We have to be practical if we expect our adjustments to be satisfactory for a year or more.
1 -
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 106 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 953 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements