Turn Down and Condensing
newinnj
newinnj Member Posts: 64
Hi,
I have a boiler with a 15:1 turndown. With "the Wall" help I am fine tuning the boiler parameters.
I was on the web and found two comments that the high turn down boilers manages things through the air gas mixture and they add more air to the mix to get the turn down. They also state that increases the dew point and might prevent the condensing boiler from condensing and loses its high efficiency. I don't know the rules of adding links in but a google search for The dirty little secret of high turndown ratios. An engineer associated with a boiler manufacturer had this on YouTube. Also found a commercial boiler service company in Nebraska had on their website of info also stating the same. Just wanted the pros opinions on this. Thanks in advance.
    EdTheHeaterMan Member Posts: 12,150
    I'm not sure what your question is exactly?
    You want to know something about a boiler you already own in relation to the 15:1 turn down ratio? What exactly do you need to know? And what will this information get you to change, if anything?
    LRCCBJ
    mattmia2 Member Posts: 16,745
    If that were the case the O2 would go up on the lowest fire. I don't really see why there would be a need to do that with the right burner geometry.
    hot_rod Member Posts: 27,446
    Keep in mind Patterson Kelly boilers start at 300,000 BTU/hr. They play mostly in the 750,000 and up range.
    A few points I would mention. He talks about the need for turbulent conditions in both the gas side and the water side. In residential sized systems, piping below 1-1/4" that would be a very low flow condition. Somewhere below .5 gpm in copper tube to go laminar.
    He mentioned that modulating boilers are mainly used to correct a piping or design deficiency. I think in residential work they are more to address zoned and micro-zoned systems. Again PK deals with larger commercial systems, so that may be more of their market, solving problem jobs.
    For years now we have been suggesting all hydronic systems should be designed to supply a design load at 120 SWT! So that keeps you in condensing range, 90+ fairly easily. In his example you may see flue gas a few degrees above return, now approaching 99% efficiencies!
    Although when I suggested 120 max. SWT, Robert Bean asked me why not 110 or 120. Always a step ahead, that boy:) His crystal ball was already presenting A2WHP potentials.
    I think the damper you see in mod cons is how they get above 10-1, the gas valve doesn't really modulate down so low, they start to chock off the air flow as he mention. That is why cleaning and keeping those dampers moving is an important part of mod con service.
    As far as 20-1 and higher, that is often two 10-1 boilers inside the jacket, both running 10-1, not necessarily one HX modulating that range. Or a HX like the Sermeta DUO 260K and up.
    I though he did a great job of making the presentation understandable.
    GGrossPC7060
  • newinnj
    Well it's a Navien NHB-150 boiler with a turndown of 15:1. By changing the space heating and DHW min heat capacity (%) down to 7% that makes the boiler (150K) be like 10,500 for minimum operation. I just was reading that with high turn down there might be an issue with boilers not condensing. Is there something that I can keep an eye out for if this is an issue or not. Some stat that the boiler has for diagnostic info or the how much the condensation pump is moving? I just did not know enough if these website postings were valid or not.
  • newinnj
    My prior post was written before everyone responded. I thought the presentation was good so that is why I asked the question. So it looks like a residential application is behaving differently than a larger commercial installation. The company in Nebraska was also a very large commercial boiler servicing company. Thanks I will keep an eye out maybe on the condensation output with various turn down percentages. Thanks I think I will follow everyone's advice and keep it as low as it goes.
    PeteA
    As the presenter noted, the return temperature is the key to condensing, or the quality of the condensing.
    The damper probably covers the a high jet or high air passage so a low jet can handle the small flows sort of how you use 2 mixing valves in parallel for a wide range of flow rates.
    PC7060
  • GGross
    GGross Member Posts: 1,885
    The issue I have seen with high turn down boilers not condensing is that the boiler is way oversized, and the installer sets the supply temperature, or the reset curve, far too high so the boiler never condenses. If the boiler is more "right size" it might still condense a bit when the supply temp is set too high, but only because it will not reach that specified supply temp during a call for heat. With an oversized high turndown boiler it will go to high fire and hit the "too high" supply temp almost immediately. This is just what I have seen going to many jobs to look over what installers actually do in the field.
    As far as the boilers not condensing on low fire? I mean I am no scientist but I have been to hundreds of installs and physically watched the burner at 10% (where possible) and can SEE the condensate so I am calling BS on that.
    GroundUpPC7060
    Most boilers have a way to limit the max firing rate and usually some other settings to make it do this less.
  • GGross
    That is a great point and something I see done only rarely out in the field. It is very much worth mentioning though!
    mattmia2LRCCBJ
    Unless you load is lower than about 8,000 btu/hr, it is almost impossible to over-size a mod con boiler. Is there a CI boiler in that btu/hr range. Is 50,000 input about as low as they go?
  • dronic123
    dronic123 Member Posts: 68
    edited March 2025
    WM cga25—-38k in and 27k out
  • LRCCBJ
    LRCCBJ Member Posts: 1,043
    You'd be incorrect on that. Just look at the IBC SF99-1. Cannot get below 15.5…………the smallest they make. Severely oversized in the shoulder seasons. You can't get it to keep running if you have a zoned system.
    he stated that he had a NBH 150, so a 10,000 btu/ hr turndown. Still lower than the CGA25 that @dronic123 noted. And you have the high 138,000 for a quick indirect recovery, if needed
  • GGross
    edited March 2025
    That's not what my point is
    Let's say I can heat my space with 130 degree water but I set the supply temperature to 180 because I am an installer in the field and I want no callbacks. An "oversized" mod/con will fire to 100% fire rate to achieve that 180 degree water as soon as it's programming will allow and I won't condense, it won't try to modulate down unless the thermostat doesn't satisfy but it's still not going to condense because I am at 180. If I set it for 130, (the temp I need on this day) the boiler will fire up to 130 and modulate down until the call ends and I will condense. My concern with oversizing isn't to do with traditional oversizing concerns, it is with setting the supply temp too high and not condensing. Unless you have some kind of indoor feedback, or a properly set outdoor reset the boiler doesn't know you set the supply temp too high. A more "correctly" sized mod/con, or one that had its high fire limited, will not be able to jump straight to 180 because it is properly sized for the load and even at 100% will usually take longer than the duration of the heat call to hit anywhere near 180. This is primarily a "design day" argument or temps close to, I understand that even a well sized boiler might be able to quickly jump temperature when it's 59f outside if the setpoint is above condensing temps
    GroundUp
  • newinnj
    Hi quick history on the boiler and one question.
    The initial boiler install was install and run. It was with the Wall help I got over some big hurdles. Now I am in a second stage of optimizing the oversize boiler.
    I have set the minimum for space heating and DHW.
    There is an option which reduces the maximum heat for space heating and DHW. I will later this year do a proper heat calc. Rough estimate need 60k btu I will like to reduce both max for space and DHW.
    The question is there any drawbacks in doing this and mechanically what is happening inside the boiler for this to be achieved?
    does your boiler have a boost function? If you crank down the SH limit too far, the boost function on some brands will notice the boiler has fallen behind and allow it to ramp up, even though you have limited the firing. It knows this by watching the run time and seeing if the SWT is increasing.
    The boilers with the more sophisticated controls can really optimize their performance.
    It take a while to dial it in, which is why the owner should know how to monitor and tweak the system, in my mind. I’d guess most mod cons are running a random setpoint temperature unless the installer really understand all the functions in the control.
    . I chose to offer only one or two brands so I could stay current and get to know the controls inside and out.
    I can’t imagine any tech being able the know the ins and outs of numerous brands and models.
    newinnj
  • newinnj
    edited March 2025
    Thanks Hot_Rod!
    I have found an old thread on max firing for others if they are interested.