Lochinvar Boiler Leaking Gas
I received an impassioned text today from a SF customer where we installed a KHB boiler 6 years ago. He said that there was a strong gas smell coming from the boiler whenever it goes into high fire. They’ve shut the boiler down until I get there in the morning.
It’s a radiator system with the boiler vented through the roof; makeup air a separate pipe from a sidewall to the outside. There’s also an indirect water heater.
Perhaps one of the PP vent connections separated even though we used lock rings. Any thoughts before I go out there?
    mattmia2 Member Posts: 16,692
    if you have an air leak anywhere between the gas valve and the combustion chamber you have a gas leak. possibly a spray bottle with sop but there is the how do you get the gaskets without getting the electrical stuff
  • I went to the jobsite this morning and sprayed leak locator solution at all of the connections after the gas valve as the smell is only there when the boiler is running. Couldn't find a leak. I then sprayed the lid of the HX at the sight glass and blower and it started bubbling, but I don't know if it's from the solution boiling or if there is an actual leak.
    I've ordered new gaskets for all the lid penetrations. Unfortunately, no one stocks Lochinvar parts out West here and they have to be ordered from the factory. Does anyone know of a stocking distributor?
    hot_rod Member Posts: 27,416
    Intermountain Sales in Salt Lake is my lochinvar rep. They keep an inventory, try them at
    801 936 0228
    Tech line 801 936 0334
    Custsvc@intsales.com
    Western Nevada Sales has a good hydronics department, I don’t know if they do Lochinvar. Reno headquarter, branch in Truckee if you want to make a ski trip and parts run☃️⛷️
    can't you run the fan without firing it in test mode?
    Lochinvar says replacement heat exchanger gaskets are 2-4 weeks out, not including shipping. Bah!
    ScottSecor
    Permatex? Looks like the nuts must have been loose?
  • Yes, the nuts were loose, but I think the real culprit is the refractory. There’s nothing to secure it to the cover plate and when I pulled out the burner, the refractory had slid over the burner. I think this caused overheating which caused the gasket to fail.
    mattmia2GGrossScottSecorGroundUp
  • tim smith
    tim smith Member Posts: 2,932
    Alan, did you get the part yet, Im sure my rep has one in stock here in Washington. I would question that the refractory was down over the burner due to the rim thats appx 1" or so down from top of heat exchanger retains the refractory from going down further. How long has it been since it was serviced? If you want PM me to talk about it and leave ph #. See attached photo
    Tim
    EBEBRATT-Ed Member Posts: 20,155
    What I hate about Mod Cons gaskets 2 weeks out + shipping time. I would call lochinvar and **** them out they would know who has gaskets in stock.
    or get a sheet of the same material and cut it out
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,088
    Hi, No doubt McMaster has the right sheet goods, and they ship fast.
    Yours, Larry
  • ScottSecor
    ScottSecor Member Posts: 1,033
    We too deal with very similar issues. Frustrating to say the least that parts are so difficult to get for a six year old boiler. In my area this boiler is considered high end, I sometimes wonder.
    Alan (California Radiant) Forbes Member Posts: 4,712
    edited March 2025
    @tim smith Yes, Tim. You are absolutely right about the refractory being sandwiched in place and I realized it as soon as I re-installed it just a couple of hours ago. This was the first time the boiler has been serviced since we installed it about 6 years ago.
    Part #100287111 for the HX gasket. I purchased the boiler at Pace Supply, but they don't stock many parts. I eventually ordered my parts list (igniters, flame probes, gaskets, etc.) from Ferguson who said some of the gaskets are "made-to-order" from Lochinvar.
    I also called the Lochinvar rep. - California Hydronics - and they were out of stock and couldn't tell me anything about availability that I didn't already know.
    Parts availability is a top priority for me as service and repair is my main gig and Lochinvar used to be my #1 replacement boiler.
    Thanks, @Larry Weingarten. I'll order some sheet goods from McMaster, but I wonder if Lochinvar or my liability insurance would cover me if something went wrong.
  • Larry Weingarten
    Hi @Alan (California Radiant) Forbes Is there any way of getting the specs on the present gasket rubber? Hardness, temperature range, etc? McMaster is good with their descriptions, so if you matched the existing specs, I'm not seeing how a lawyer could cause trouble. I suppose you could get a written agreement from the owner letting them make the choice between waiting for heat, or proceeding with letting you cut a gasket… I'll take my attorney hat off now. 🤠
    Yours, Larry
    I spoke with Intermountain Sales in SLC, they have the gasket kits on the shelf. I sent the part number and pic you indicated, but have the model and serial number also to confirm, if you contact them.
    mattmia2EBEBRATT-EdAlan (California Radiant) Forbes
  • Thank you, hot rod. Tim Smith up in Seattle was also able to bird dog the part for me and it arrived today from Suntoya. I also needed the refractory and they had both. We just got back from The City now and the boiler has new life.
    Larry Weingartenmattmia2EBEBRATT-EdHeatingHelp.com
  • pedmec
    pedmec Member Posts: 1,326
    FIA, Inc in Woburn Massachusetts is our Lochinvar rep in the Boston area and stocks a lot of Lochinvar parts. if all else fails you can try them. 617-938-8900
  • tocker
    tocker Member Posts: 38
    Curious to know how this saga ended? Did you find the source of the leak? I detect a faint gas smell at/under the fan of my WHB110N periodically when it is firing.
  • The new gasket fixed the leak.
    If I were you, I'd find someone with a combustion analyzer to check for carbon monoxide in and around the boiler. You should also have 21% oxygen and 0% CO2. Replace the HX gasket if there is leakage and inspect the cover plate for warpage.
    a combustible gas detector would be great to have for that too. could also use soap.
