steam heat exchanger
what is the difference between a conbraco 37-202-01 steam vacuum relief valve
and a #62 vacuum breaker for steam
    EBEBRATT-Ed Member Posts: 19,891
    They both do the same job. The Hoffman is rated for high enough temp for steam. Don't know about the Conbraco
    Mad Dog_2
  • creger.robert
    creger.robert Member Posts: 108
    thank you
  • Pumpguy
    Pumpguy Member Posts: 794
    Not familiar with the Conbraco. From what I see online, it appears to a simple non-adjustable vacuum breaker.
    The Hoffman is a spring loaded adjustable vacuum relief valve. This has a pair of adjusting nuts allowing you to set the break point at which the valve will open to allow atmospheric air to enter to prevent going to a higher vacuum.
    Also, the Hoffman has a renewal O ring on the valve stem.
    Nothing is listed about either valves venting flow rate in terms of CFM.
    If something better is needed, let me know. Attached is a file on Vacuum Sentry vacuum relief valves. I think they're better, but it depends on what you really need.
    The attached files have details.
  • creger.robert
    thank you
  • creger.robert
    conbraco is 16 cfm