How Does This Look?

laykelane
laykelane Member Posts: 9

Just installed a boiler attempting to use the “pumping away” method for the first time, and it worked like a charm! Didn’t have to bleed a single radiator. Curious if some of you pros could offer some helpful criticism of my install and what could be done better.

Mad Dog_2

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,106
    edited February 15

    first pic looks old

    second looks like someone left their tool all over the boiler

    and third look new

    EDIT: well done

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    laykelanemattmia2LRCCBJ
  • clammy
    clammy Member Posts: 3,204

    Looks good but where the backflow preventor and a electronic low water cut off unless its equipped w a digital aquastat w a lwco feature ,both are code in my area if getting inspected . Other wise welcome to doing it the correct way now dont fall back into old habits . Its a wonderful thing when ya don't have to remove convector covers to bleed rads and convectors . on another note if looking to get better try califee demineralizing filter to bring your fill water within what the manufacture's specs . Keep up the good work .

    peace and good luck clammy

    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating

    EdTheHeaterManMad Dog_2mattmia2LRCCBJ
  • hot_rod
    hot_rod Member Posts: 24,390

    a nice clean installation, every component in the correct location. Should serve you well.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    laykelaneLRCCBJ
  • laykelane
    laykelane Member Posts: 9

    Thanks Clammy!

    The backflow is right after the ball valve on the feed line if you zoom in. LWCO isn’t required in our area unless it’s steam. The control board has an LED with “LWCO” next to it. Not sure how to identify if it has one built in or not. How would I verify that? I’m a plumber trying to get more into the heating side, and have very little personal resources at my disposal beyond books, so have lots of questions.

  • laykelane
    laykelane Member Posts: 9

    Thank you!

  • hot_rod
    hot_rod Member Posts: 24,390

    It adds time and cost, but running a cleaner, flushing and adding a treatment is another good step. You want the insides as clean as the outsides :) Smallsquirt cans like this make it a simple job to ad the chemicals.

    Testing the fill water is a good step also. The installation manual will show the water spec.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,106
    edited February 15

    The new CGa from Weil McLain is equipped with a LWCO that is connected to the boiler control part number 381-330-039. the sensor is part number 591-391-995

    You don't want to be that guy that only does the "Minimum Required", do you? You used a micro-bubble air separator, which is a step above the minimum Air Scoop. That makes for a better system, and trouble free purging and constant air removal over the season. If your boiler does not have a LWCO included, then add one to the system. You might want to look into the Modulating Condensing boilers to save your customers even more on operating cost.

    Good luck with your quest to be a better heating professional. God known that we need more of you!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • laykelane
    laykelane Member Posts: 9

    Thanks Ed!

    My trouble is that Im so new at this, and fairly unfamiliar with control wiring I always revert to “keep it simple” more for my own benefit. I need to learn more about controls, and wiring so I can feel more confident about this stuff.

    I’ve never touched a ModCon boiler beyond a Weil Mcclain Ultra that I could never get to run right early in my career and made me scared of them lol.

    I will say as a plumber, I fix/install tankless water heaters so I have at least that much familiarity with them, but never been around these types of radiant systems i see pictures of with all the primary/secondary piping and whatnot. Intimidating to me because I don’t have anyone here to fall back on if I get stuck, beyond tech support and books.

  • hot_rod
    hot_rod Member Posts: 24,390

    Cast iron radiators? How did you size the replacement boiler?

    The first step with a replacement is to size the boiler to the load of the home as it exists today. If any upgrades have been made to the home the load may be lower than it was, which could indicate a smaller boiler.

    Boilers tended to be over-sized often.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,733

    Your work is Stellar...neat as a pin..Great soldering job! Mad Dog

    laykelaneLong Beach Ed
  • laykelane
    laykelane Member Posts: 9

    it’s all fin tube baseboard. Old boiler was 150,000 btu. I called our supply house and their boiler guy had me measure all the baseboard, asked the sq ft of the house, and how many windows and came up with that CGA-5 as a replacement which was smaller than the original.

  • hot_rod
    hot_rod Member Posts: 24,390
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • laykelane
    laykelane Member Posts: 9

    Been about a week ago now but if I remember right it was 154 ft. House was 2 stories on a slab, and living room was huge with windows so large they were basically walls. 1971 construction.

  • mattmia2
    mattmia2 Member Posts: 11,667

    that glass is going to take a ton of heat but doing a heat loss calculation is the way to size the boiler.

    laykelane