Add air to water heat pump to radiant heating system
Hi, I am looking for advise on ho
w to add a air to water heat pump to my radiant floor heating system running on a propane boiler. Buffer tank that was sent is 2 port. Anyone has any advise in how to pipe it all up? Here is design I got do far.
If you have a tank with enough connections a 3 pipe buffer gives you a bit more efficiency. We talk about it in this Idronics issue
Consider a plate HX between the HP indoor module and the buffer. So you don't have to glycol the entire system.
Your 2 pipe drawing is correct if you go that route, still consider the HX.
I downloaded the SWEP HX sizer software. Alicia and Nathan at SWEP walked me through a couple sizing examples, on a phone call.
Living the hydronic dream1 -
My buffer tank onky has 2 port. Thaught was ordering a 4 port but ended up getting a 2 port.
Also, i should have mentionned, the whole system is running water. Heat pump is a split system so refrigerant is running from outside to the indoor unit ( prettymuch is a refrigerant to water plate echange). Then circulating water to buffer tank from there.
I am understandibg there are concerns with 2 port buffer tanks that cold water may try to run trough unused boilers, and adding check valve may offer resistance and prevent that.
2 pipe works fine. You show checks on both sides of the boiler. The circulator may have a check? Add a spring check on the other side.
A pressure gauge on tank, maybe an additional 30 lb relief valve also, in case the boiler gets valved off. Maybe the HP IDU has a relief inside?
I do not believe that heat pump as relief valve, this would be added anywhere in the heat pump loop? The gas boiler does have a 30 lbs relief valve already.
My HP came with a tee and relief valve to be installed on the job.
You want to make sure there is a relief to protect all the components should one of them be valved off.
If the boiler ever got valved off, and the only relief is on the boiler, the HP and tank are not protected.
With that 53 gallon buffer and all the piping, make sure to run the expansion tank sizer program. Amtrol and Wessel have free sizers at their websites.
Or long hand calc with the Amtrol Engineering Handbook :)
The question is, who's in control?
What's more important than how it's plumbed is how it's controlled. Do you want to be able to switch between the two systems, with only one ever running at a time, or do you want to be able to have them "help" each other out?
If it's the second, the heat pump has to be in control. Any heat pump worth installing has a variable speed compressor that modulates to meet the load. If there is also a propane boiler in there that it's not controlling it's not going to be able to sense the load, and as soon as the propane kicks on it's going to shut off.
Heat pumps that can control a boiler are rare. There was discussion of one here fairly recently, I think it was sold by US Boiler.
Plan for controll is heat pump has option to controll a electric backup, sending 240V. This will be feeding a relay controlling the heat pump. That is plan A. Plan B is if this does not work, all controls will go into a hbc eco-0600. It is design to controll staging of and bavkup switching between multiple heat pumps or boilers.
Your drawing shows an external pump. There is no pump inside the unit? You generally want a speed controlled pump with these, if not built in, they usually have a 0-10v or PWM output for controlling one. You can use the + variant of these as it has 0-10v control:
Heat pumps are similar to mod cons as efficiency is all about temperature except with a heat pumps the efficiency hit is much larger (order 20% to 50%). You always want it to supply the coldest water your place needs and you are never mixing down the supply water with any return, so make sure you don't overpump the emitters. Outdoor reset is your friend, set up properly.
You can also get a bit of efficiency boost if those zones valves can be set to bypass flow when closed. This way some heat will always be provided to all zones but you still have control over temperature.
So, for the relief valve, should we just connect one on say, thr cold water return at the buffer tank where all systems would be protected?.
And heat pump has a 240V output relay to controll a pump. Pwm provided on my unit
yes a relief on the buffer protects whatever device is hydraulically connected.
The boiler generally have a factory supplied relief. Sometimes it is installed, sometimes the fittings are in the box. Install that one as the manual shows. That is your warranty protection as well as a code required safety
Find out what the PWM signal is. Most 0..10V is fine with either 10V or 12V PWM, you can also put a simple RC filter on the PWM output to turn it into an analog signal. If the 0..10 is not an option, you might be able to get close enough control by tweaking a delta T circulator.
I used an RIB relay with a 240V coil to drive a 120V pump.
Using the 220V out from the heat pump to control a boiler might work. The only thing I would worry about is short-cycling, the heat pump is expecting the device it's controlling to be an electrical resistance element that doesn't care how long it's on for. This is basically how heat pumps that have a boiler control work, except they're aware that the thing they're controlling is a boiler.
A multi-stage thermostat is going to give issues. Think about how a boiler is normally controlled. The thermostat turns the circulator and/or zone valves on and off. The aquastat in the boiler is set to hold a certain temperature, when it needs to it fires on and off. The thermostat isn't controlling whether the boiler fires. Air to water heat pumps operate similarly to boilers, the thermostat doesn't control the heat pump, it controls the valves and circulator. The heat pump looks at the temperature of the returning water to decide whether to run. Any heat pump worth installing is going to have an additional wrinkle, where it modulates to meet the load, so it's going to be looking at the flow and return temperature to try and estimate the load and meet it. If you throw in a boiler on the same circuit that the heat pump doesn't know about it's going to mis-estimate the load, it's going to think it's a lot lower than it really is and reduce its output. When the return water doesn't get much colder it's going to reduce further, until it shuts off.
What is the make & model of the heat pump?
Luke Stodola0 -
it is a chinese from alibaba. "Fantastic" FE IHCDO8OSS
It would be helpful to get the I&O manuals
This os fhe wiring schematic
you do have an electric heat relay connection. A manual that explains the operation would be helpful
Luckily you have a reactor on the upper left side🤓
My AWHP toggles the aux heat relay a fair bit when enabled. Not something I would use to kick in the boiler.
Your boiler might have the option of a remote sensor. If you can install this on the top port of the buffer tank and set the boiler to have an ODR curve that is a bit bellow the heat pump (ie boiler targets 35C when AWHP targets 40C). This way the boiler would only kick in when the heat pump can't keep up.
Overall, I think the simplest option is to manually select between the two.
I know, i will only figure out once I power it up I guess. The mnual sqys nothing about the backup configuration. Like I said before thats plqn A. But if I dont like how it handles it, plan B is a 3rd party controller for both.
There isn't a third-party controller that will control both. Air-to-water heat pumps aren't controlled like air-to-air heat pumps.
Kaos' idea of using outdoor reset it interesting. If you have two boiler-type devices on the same circuit, the one with the higher aquastat setting will always fire first, the other one will only fire if the first one can't meet the load. If both devices have outdoor reset, but their curves have different steepness, you could set it up so the heat pump has a higher setting when it's warm out and the boiler has a higher setting when it's cold.
But that's a lot of work and may not work as intended.
I guess the question is, what are you trying to do? Is it:
- Use the boiler instead of the heat pump at temperatures when the boiler fuel is cheaper than electricity?
- Use the boiler to supplement the heat pump at temperatures when the heat pump lacks capacity to meet the heating load?
- Use the boiler to boost the water temperature at outdoor temperatures when the indoor radiation lacks the capacity to meet the heating load at the water temperature the heat pump is capable of providing?
- Use the boiler as a backup in case the heat pump is unavailable?
Each of those would require a different control strategy.
That looks like a price point unit, so probably not a feature rich controller.
The US Boiler A2WHP seems to have the most "developed" controller, nicely packaged also. I expect to see more innovation at AHR this year as the off shore manufacturers continue to adapt to US needs and wants.
Viessmann has always been a well though out control on their boilers. But early versions came with 30- 50 pages of instructions! In Genglish :)
We went through this with Resol solar controls, the MX a PLC type control, was too complicated for most to understand. Tech support would spend hours on the phone with configuration help.
So there is a balance to find on a "do all" control
There actually are a few controllers that do just that, the hbx eco-0600 gives all these options. Mainly boiler will be to backup at either lower temp outside, or if heat pumps fails.
Yeah, Curtis at HBX has been paying attention and trying to cover all the control options for A2WHPs. If you send him ideas he prototypes quickly.
From the HBX website:
"The ECO-0600 can control up to four (4) heat pump stages (air-to-water or water-water) or chillers and a reversing valve with outdoor temperature reset control."
The heat pump you've selected is not a multi-stage heat pump, from the info you've posted it's clearly a modulating heat pump with a variable speed compressor. It doesn't run from an indoor thermostat, it modulates its output based upon what it perceives the load to be based upon the flow and return water temperature.
The US Boiler controller that @hot_rod alludes to above is the only one I'm aware of that allows a modulating heat pump to bring in a boiler to boost its output.
The SpacePak Soltice controller has evolved with Jim Bashford their national sales and training manager, being a former contractor's input.
I think Enertech also keeps the HP online and supplements it with a backup source, instead of dropping it off. They also suggest a buffer tank is not needed.
These A2WHP controls are evolving quickly as data comes in from the field.
Keep looking around for the most current information.
I'm not aware of any solution that's not specific to the brand of heat pump, and I wouldn't expect one until a standard develops for the heat pump to communicate with a controller.
@hot_rod: "I think Enertech also keeps the HP online and supplements it with a backup source, instead of dropping it off. They also suggest a buffer tank is not needed."
I watched another video with Siegenthaler (link below) and he says "in most applications" a buffer tank is not needed. Which makes me even more curious as to how they do it — and what those applications are.
I have noticed that when my heat pump goes into defrost mode it steals heat from the buffer tank, which would otherwise be coming from the house. So there is a justification for it sometimes at least.
John Siegenthaler & Michael Ridler Discuss Enertech Air to Water
Here is manual I have. I see a few examples where this heat pump is controlled by thermostat. It would be in the eco-0600 as a single stage heat pump, and then the heat pump would handle the modulation I believe. The controll would be used in the "on/off" port of heat pump and act as a thermostat. So the hbx would tell heat pump when there is a demand and turn it off when we do not want it operating, and would also be able to kick in the boiler when required.
it just come down to to how far you want to chase ultimate efficiency. While keeping warm, of course.
So one way is to calculate when the HP cost more to operate than the gas or other backup heat source.
How to know that, what control makes the switch back and forth.
To that end, you would want heat emitters that perform at low supply temperature. Radiant panels, floors, walls and ceilings are among the best.
Generously sized panel radiators can work well also. It.s a surface area game to heat with low temperatures.
Then look at the performance data of the HP. Hoping it was actually done accurately, not by the marketing team😁
In some cases until you have it installed and running it is a guesstimate on how to assemble and control the system to your specific wants and need,
I’m several months into my Viessmann system and I still have questions on control modifications, tinkering with the hydraulics to maximize the performance.
I run a buffer at 115, constantly. It works well, but ODR will probably add a bit more efficiency, once I dial it in.
My problem with any of the fancier controls is the cost is high enough that the ROI is pretty much never. Never mind the time it takes to set up and tweak.
Around me propane is just a bit cheaper than resistance heat, so running the heat pump as much as possible is the best cost.
I would be tempted to plumb the setup with the boiler on closed spaced Ts after the AWHP. Set the AWHP circulator to run all the time. This way if the heat pump can't keep up or shuts down, the boiler will automatically pick up the load and supply heat as needed. Will need to tweak some boiler curves and settings to make it work.
As for turning the AWHP, on/off, not the best idea for efficiency. You want this running 24/7, with the right reset curve some of your zones will always be calling for heat anyway. There is really no need to control the AWHP directly, just set the reset curve and turn it on and let it do its thing. Your zones will take heat as needed. This is pretty much how I run mine.0 -
@Kaos: "You want this running 24/7, with the right reset curve some of your zones will always be calling for heat anyway. There is really no need to control the AWHP directly, just set the reset curve and turn it on and let it do its thing. Your zones will take heat as needed. This is pretty much how I run mine."
This is really the key. The whole point of having a heat pump with a variable-speed compressor is that it can modulate its output, it works best when it is running continuously at a level matched exactly to the load.
How does it detect the load? The emitters inside the house have to have some way of modulating the amount of heat they put out. If you have passive devices like radiators or under-floor heat that can be done with outdoor reset or zone valves, if you have active devices like fan coil units it can be done by modulating the fan speed with a local thermostat. If the emitters are varying their output to match the load, the heat pump can detect how much heat they are dissipating by looking at the leaving water temperature and return water temperature, and the flow, and adjusting the compressor speed accordingly.
If you look at the wiring diagram provided, the thermostat doesn't plug directly into the heat pump. The thermostat (or really, thermostats) controls the zone valve and the end switch on the zone valve controls the circulator.
If you were to put a boiler on the circuit, with a multistage thermostat*, if the heat pump weren't keeping up and the second stage fires, the boiler turns on and the heat pump starts seeing warmer water in its return. This would cause the heat pump to turn down, and eventually turn off. It would stay off until the boiler shuts off because the thermostat is satisfied and the water has cooled off enough to let the heat pump run again. If the behavior you want is the boiler backstopping the heat pump that wouldn't be happening, rather the boiler would be taking over and shutting off the heat pump.
In heat pumps where this kind of backing up is successfully implemented, it's done in the heat pump internal controller. The heat pump sees from monitoring the load that it's not meeting the load and so it calls for the boiler. It also knows that it has called for the boiler, so it keeps that in mind when assessing the load.
*(A related question is how you would configure multistage thermostats in a system with multiple zones. Does the second stage fire when one zone calls for the second stage? All of the zones? Most of the zones?)
The piping schematic looks good. You'll need to have multiple purge valves.
I personally would be hesitant to use the 2 port buffer tank as opposed to 4 port or 6 port. But it'll probably work just fine how you have specified. Is there a separate port for the pressure relief valve near top of tank ? That could be teed into for a another port. A larger buffer tank will act as a larger "thermal battery" and can, in theory, minimize the frequency the boiler needs activated.
What software did you use to make that schematic?
- 110 Chimneys & Flues
- 978 Plumbing
- 387 Solar
- 17 Recall Announcements