Rinnai tankless cycles on when toilets are flushed.
Installer changed 1/2" water lines to 3/4" during installation. Everything working fine except when toilets are flushed, tankless unit blower cycles on for a short period of time.
Anyhelp would be appreciated.
Every toilet in house? Does this happen when you turn cold on to bathtub?
Do you have hot water recirculation? Dedicated recirculation line or a crossover valve that uses cold water line as return?
Not all toilets, just the downstairs one, and yes, the unit cycles after turning on the cold water for the bath tub.
No hot water recirc lines and only two mixing valves, one in the downstairs shower and the other is the kitchen sink.
Yes first check for a cross and make sure you don't have crazy high water pressure.
This is a nice instructional:
https://www.prostarmechanical.com/blog/plumbingcrossover
Mixing valves with no checks or without functional checks are a common source for crossover.
Toilet anti-sweat valve causing the cross?
Here's a thought. Is the toilet piped with hot water?
Flush the toilet a half a dozen times or more letting the tank fill each time and then feel the pipe under the tank and the water. Is it hot?
What model mixing valve is installed? An ASSE 1070 comes with check valves. They are required as part of the listing.
Some valves have dual listings ASSE 1017, point of distribution, and ASSE 1070 point of use. Those models will have two checks in the box also.
Cross connecton test done to no avail. Followed the instructional link, thanks bjohnhy, and everything seem ok. The hot water is shut off to the washing machine so mixing valve {solenoid} is isolated. Both toilets are confirmed plumbed with cold water as well.
I will change the cartridges in both the single handled faucets for the shower {MOEN} and the kitchen sink {BLANCO}.
I appreciate all the assistance.
I thought it was a check valve issue the first time I flushed the toilet or turned on the outside faucet for the hose and the units fan cycled on for a few seconds.
I contacted the installer and requested a check valve be installed on the cold feed prior to the isolation valve on the unit which he did beause I hadn't paid for the installation yet. That did not solve the problem.
Could the problem be: 3/4" city water line to house…shutoff valve…city water meter…shutoff valve reducing internal water lines to 1/2" throughout the house…increased to 3/4" ahead of tankless and then reduced back to 1/2" for tie-in ?
You can try to close the cold water supply to the toilet a bit to reduce the flow there, just enough that it doesn't trigger the flow sensor on the unit. With 1/2" pipes, this had the added benefit of limiting the toilet flush/ scolding while showering issues.
P.S. A big water pressure improvement with 1/2" setup is to replace the cold water pipe from the meter up to where your cold water starts branching off and to the water heater with 3/4". You can leave the rest 1/2".
