4 Way Mixing Valve Education!
Cyclist77
Cyclist77 Member Posts: 259
I currently have a Tekmar 3 Way Mixing valve on my radiant heating system using a coal stoker boiler. Looking to understand 4 Way Mixing Valves. Is this screen shot a good representation?
    hot_rod Member Posts: 27,495
    The main difference with a 4 port is you get two mixing points inside the valve. So it can both mix down a temperature for a low temperature, and mix up the return to the boiler to protect it from low return temperature.
    They were very common with copper tube and cast iron boilers connected to low temperature radiant.
    But to be effective they need an actuator with sensors that react to two temperatures.
    ODR was another function built into many of the controls that run the actuators.
    Many of the mod con boilers have functions onboard now also to send a signal to a mix valve actuator.
    Here is a look inside to understand the difference between 3 and 4 port mix valves.
  • Cyclist77
    Bob,
    So with a 4 way it would have a way to sense outdoor temp as 1 of the temps?
  • Cyclist77
    Can a 4 way just be operated manually a d not have an Actuator?
    yes to both questions the ODR is usually in the actuator. Some valves, like Taco have the control built into the actuator
    Without an operator it is considered a “dumb” valve It can only respond to manual input
  • Cyclist77
    Dumb valve -perfect for me!😀