Three 1/2” copper pipes coming out of a manifold and a threaded rod center support.
I think they are sealed. They are on every dry return before they drop
Comments
-
Single pipe system?
Some kind of vent that is up in between the joist space. Too dark to see what is just below the ceiling… OR do they go thru the floor above and have something else connected up there?
Need a Flash Camera or a better light.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Looks like it might be the vent on a Mouat system. @gerry gill ?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
sorry, I only had my phone and it would not flash … will try again. It is a 2 pipe steam system with mains and parallel dry returns that drop to wet returns on their way back to the boiler
there are 3 pipes that have a common cap that is held on by the center threaded rod.
The top part is shaped like a fidget spinner and I felt the top and did not find any holes or vent. Very similar to anti-hammer cushions in a water system.
Top of it looks like this with a hole in the center for the threaded rod…seems like this is a cap with no flow between the pipes
0 -
as bright as I could make it
0 -
@TKPK , that really is an air vent. You have a Mouat Vapor system. Go here for pics and discussion of a similar unit:
https://forum.heatinghelp.com/discussion/139551/more-mouat
Hopefully @gerry gill will chime in- he is our resident Mouat guru.
Where are you located?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
That looks like the same place with less lath.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
the lath is there, just not in the picture provided. You do see a little bit of the knob and tube though.
1928 house in Grosse pointe park MI.
Unfortunately it got removed before I got any pictures but this house had a coal ash carousel that was below floor grade so you (meaning servants?) could empty the ash when convenient. Storm drains backed up and it became a pond and it rusted almost beyond recognition.
0 -
100%
Read the patent and understand them as condensing tubes with air escape at the top (likely on the side of the tube below the cap) and capillary tube at the manifold.
The column of water, if any, has to equal the pressure of the boiler.
very nice … no risk of these being removed in this house. I knew this group would not be stumped!
This is a friend’s house with a newly installed boiler this season. I turned the pressuretrol down to the minimum from its factory setting.
0 -
You really need to put a Vaporstat on that boiler. Mouats don't need more than a few ounces.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
exactly what I told my friend.
leave the pressuretrol as a safety only device and wire a vaporstat in series?
0 -
If you wish- can't hurt. But they should be on different pigtails, so if one clogs the other might still work.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements