Damaged Beckett air tube
found this in a Burnham PV83S I serviced this week. the condition of the fire box isn't the worst I've seen but the air tube shroud looks like someone beat it with a hammer. the target wall insulation was leaning way into the chamber. I'm assuming the damage to the shroud was cased by heat being reflected back onto the burner. Am I right?
I cleaned it and got the insulation back in place and got the crud out of the air tube.
I was surprised to get reasonable Combustion results, expecting to get impingement on the shroud or at least bad air flow.:
Tstack 456
o2 4.9
CO 15 PPM
Ex Air 28.5
CO2 12.03
Smoke 0
I convinced the owner to let me replace the air tube and and insulation.
Comments
-
Not my first time seeing something like this. Whoever was "maintaining" that boiler was taking the customer's money.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
Considering the end of that tube, at first I didn't believe I could get there.
0 -
so do you think the dammage to the shroud was caused by heat?