Steam Boiler Installation
Paul S_3
Paul S_3 Member Posts: 1,292
Hey guys, we haven't posted one of our installations in a while. Removed a 400k btuh Peerless boiler. Installed a EG-65. 4in drop header and vaporstat. Home has 608 Sq Ft of EDR. Ran new wet return and split 2 dry returns that were connected above the water line and installed 2 Big mouths. We used some stainless nipples and bushings at boiler return connection. Installed a 1 in loop seal for pressure controllers.
IMG_20241123_153054.jpg IMG_20241123_153057.jpg IMG_20241123_153100.jpg IMG_20241123_153103.jpg IMG_20241123_153107.jpg IMG_20241123_153116.jpg
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
PC7060EdTheHeaterManHeatingHelp.comWaher
  • delcrossv
    delcrossv Member Posts: 2,193
    King valves even! Nice!
    Paul S_3
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,827
    edited November 2024
    … and a fitting to flush the returns. This is one beautiful piece of work.
    I don't know how you find customers who understand and are willing to buy this level of quality.
    delcrossv
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,563
    Very nice. I am not fond of horizontal piping on The equalizer. But if it's all pitched, then all is good
    Long Beach Ed
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,691
    Superb! Thanks.
    Retired and loving it.
  • Paul S_3
    Thank you guys. @STEAM DOCTOR yes, I'm not fond of the horizontal equalizer either. One of the younger guys connected it. It is pitched.
    347-692-4777
    ASMHVACNYC.COM
    STEAM DOCTOR
  • pedmec
    pedmec Member Posts: 1,295
    Not to nit pick but that equalizer should have been straight down. i would be surprised if that doesn't give you water hammer. i think with a little more foresight you could have eliminated the horizontal runs and gotten away with 45's out of the header. All that horizontal piping on the riser out of the header is going to cause all the steam that condenses in that piping to have fall back on to the header.