2nd Zone on Monoflow heats whole house
My 1968-built ranch is heated by a monoflow system with a Navien (gas) tankless boiler.
I created a 450 sq ft office/gym in my basement (I work from home) and my plumber installed a second zone on the monoflow system to heat it.
No surprise, when Zone 2 calls for heat, it prompts the whole house to heat up. In the attempt to keep the basement room at 68 degrees, the upstairs would be pushing 10 degrees above that.
He came back and installed a tee in an effort to prevent the return from heating the whole house, and it has improved, but the upstair's cast iron baseboards still get warm when zone 2 calls for heat and the upstair's thermostat is off.
He is good plumber, but admits to not being well-versed in monoflow systems. He is looking into the problem, so I thought I should as well. I just cannot speak to his level on exactly what he has done.
I can provide photos of the setup and consult with him on anyone's question, but I would like the get this settled prior to the New England winter.
Thanks in advance.
MonoFlo® systems are a special breed of well designed systems that use pressure differential to make the heat go where it is supposed to.
- Are your original radiators Convectors or Baseboard or cast iron?
- did the additional basement radiators connect to the same one pipe main?
- Did he put a thermostat in the basement
- Does the basement thermostat operate a separate zone valve or a separate circulator pump?
A diagram of YOUR pipe design (original) and the added pipes would be helpful
This is a typical MonoFlo® design
The special Tee Fitting is usually found on the return side of each radiator. That tee fitting causes the water flow in the one pipe main to be restricted a little, making the path going to the radiator an alternate route for the heated water to flow into the radiator. Most of the water will continue thru the main with a percentage heating the radiator. If the balance of that pressure drop is interfered with, then you can have heat going where it is not supposed to and no heat where you want heat.
If your plumber added a separate zone with a separate circulator and did not include Flo-check valves, then the pressure from one zone circulator can force reverse flow thru the other zone if that pump is off. That can add heat where you don't want it from time to time
The green zone represents the basement loop with a second circulator pump operated by a separate thermostat. Is your system at all like this diagram?
2 -
Ed
To answer your questions:
original radiators are cast iron baseboards, basement is new slantfin-styeled baseboard element.
I would say yes, it looks that way (see photos)
Yes
Yes
This photo shows his first connection (dark gray) to the baseboard below (from the main pipe). The lighter gray pipe is to alter the return (my understanding).
This photo shows the two zones.
This photo shows his original connection (dark gray) to the boiler.
This photo shows shows the new connection (lighter gray). My understanding is there is some trap or something that is supposed to alter the return. Again, my understanding is very limited.
Hopefully, this sheds some light. I can take photos of anything you folks need to help me out.
Delcross
It doesn't like he installed any of those.
You're ghosting your other zone. Note @EdTheHeaterMan 's diagram above where it says "flow check"
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.1 -
Here is some information from this book https://s3.amazonaws.com/s3.supplyhouse.com/product_files/108119-Reference%20Guide.pdf that will help your plumber understand about Zoning With Circulators
Let your plumber have the link to this book, it is an easy to read informational coverage of your situation, that I read several times until I had a full grasp on the topic. I used it as the textbook for the one day seminar I used to teach.
This is old school ways to do stuff, it was written in the 1960s. There are newer ideas that may have improved the way we do things today, but your system is from 1968 with a new boiler connected to it. That worked well until the additional zone was added. I believe the Flow Check valves (or lack there of) are the reason you are having the issue.
You have 2 potions here. The valves need to be added OR you may be able to add the Flo-Check vlave like this to your existing pump.
Based on the limited photos. and assuming that you actually have a MonoFlo® one pipe system, I believe that this is your piping system before the added zone.
The above illustration is the design that Navien manual would suggest for your system. That includes 2 circulator pumps. One for the boiler and one for the system. If you do not have that near boiler piping design, then you may have this design (before the basement zone)
Notice in the Red oval, the boiler pump is missing and the Navian manifold is missing. This may work on a one zone system, however it will not work on a multi zone system.
Assuming you have the upper illustration properly designed near boiler piping, this next diagram is how you should add an additional zone.
Take note that the new zone circulator pump is TEEd off of the main AFTER the expansion tank. It can also be AFTER the existing system circulator pump TEE (But not after the actual pump).
I hope this helps your plumber.
These are the three T's that were added to create the second zone. Are these are not monoflow T's? I assume the one attached to the circulator is not, but the other two?
Thank you all for your expetise. Much appreciated.
You definitely have Diverter tees. (not MonoFlo® brand) in the photos you just sent.
It is difficult to tell what you have other than the Tees and some circulators. I would like to see some of the original tees (before the additional zone) to verify that the original system is also a Monoflo® or diverter tee system. Also can you step back about 8 feet from the system and take some pics so we can see all the near boiler piping. That way I don't have to guess at what piping you might have.
It is like guessing what kind of car you have based on these photos.
They don't show the whole car, so I can't tell you how to fix it. I can only guess and hope that you understand my illustrations.
Hopefully these are clear enough to tell a better story. I zoomed in on the piping below on one of them. Let me what else I can snap. Thanks.
Wrong …..
Every new photo gives more information. Thanks
Well I can see from your new photos that you have an older design NCB model Combination Heating boiler and Tankless Water Heater. I can also see that the installer used the primary / secondary optional Navian manifold. That is a good thing. I still don't know if you really have a MonoFlo® system. That would be determined by the next 6 fittings that are on the pipe leaving the boiler indicated by the Red Line
I can see that the new zone was connected incorrectly to the main system piping as indicated in one of my previous diagrams and shown here.
When possible Can you show a picture of the next 6 fittings on the pipe leaving the near boiler area, (on the red pipe) and a picture of the old original radiators
This is a representation of what I can guess is your system as it is installed now
Thanks Ed, I agree, that is pretty much it.
I just took photos of those fittings you asked for, but I need to organize them before posting. It is a maze down here.
The first Tee off the main pipe from furnace breaks away from this crazy loop setup that was part of an old oil system and heads to first radiator tee.
This 2nd tee was added for the basement zone, which was soon capped off so another loop cold be added (mentioned earlier). There was another (capped) tee (not shown) that went to that now removed oil-fueled boiler.
This is the first tee off the main that heads upstairs to first radiator, a 90-degree, two-walled baseboard for living room.
This tee on the left goes up then heads left to the wall and up to connect to opposite end of 90 degree living room radiator.
The two tees on the right are the opposites ends of the 2nd radiator in living room. The one far left is the one shown above.
I could go on and on and send photos of the tees for every radiator in the house, but I think you get the picture.
Hi All,
New member here.
I have read through this thread and plan to run a 2nd loop off of my current monoflo system.
i have a weil Mclain furnace - and had it stubbed out for a future 2nd loop to be ready for adding a 2nd when i do my basement.
I see and understand much of the diagrams and descriptions above.
MY QUESTION IS:
Will this Taco circulator act as both the circulator AND flow check? (see link below.)
https://www.homedepot.com/p/Taco-Comfort-Solutions-1-20-HP-Three-Speed-Cast-Iron-Hydronic-Circulator-with-Integral-Flow-Check-0015-MSF3-IFC/321298384
Or is it required to have an isolated flow check on each loop? I will have to see if the other existing circulator has the 'integral flow check' on it (or if there is one on the loop).
TIA!
Additionally, to my post immediately above:
My basement and 1st level are on 1 loop, and fairly balanced. Refinishing my basement and adding insulation may cause this to get unbalanced and is why i am planning to run it on its own zone.
what is the recommended best (or affordable) way to create a 2nd zone?
-valve controlled? on 1 loop (probably have 8 baseboards up stairs) and 1 wall (build out) heater and 1 large cast iron in the basement. (which when refinished would have 5 rooms/heaters)
-2 loops each with dedicated circ motor? (my boiler has a manifold ready to got for this); i think i can achieve this with a 'switching relay' and additional thermostat & circ motor to the the existing hydrostat on the boiler; correct?
-non wired therm valves?
- Currently have a single monoflo - running 2 floors (1st level and basement) - fairly balanced 'as-is'
- redoing basement and will have access to about 75% of the loop with planned demo… basically, 1 room is finished (not being demo'd) and i was planning on replacing that wall heater with a baseboard and removing wall buildout heater, and splicing the leads to not lose flow on the existing loop.
Thanks again!
Hay @JimmyGunz . you should start a new discussion. You can refer to this discussion in your NEW discussion buy copying and pasting this URL
https://forum.heatinghelp.com/discussion/198288/2nd-zone-on-monoflow-heats-whole-house
When you copy and paste it then hit return it will look like this:
Then ask your questions there. That will be less confusing.
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 111 Geothermal
- 163 Indoor-Air Quality
- 72 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 55 Water Quality
- 47 Industry Classes
