Weil-McClain PILOT orifice
Hi all,
I have an older Weil-Mclain PEG-40, natural gas, 125,000 btu with spark ignition and mercury flame sensor. Does anyone have a part-number manual that includes the electronic controls, ignition, Pilot etc. The only manual I found online has only the sheet metal, boiler sections and related parts.
I'm trying to find What the gas Pilot orifice size isand Part Number for the orifice ?
Thanks.
Note 1: Order sufficient quantities to replace all orifices within a base.
Page 33 of the manual:
chrome-extension://efaidnbmnnnibpcajpcglclefindmkaj/https://www.weil-mclain.com/sites/default/files/field-file/eg-peg-egh-series-4-manual_1.pdf
Thanks for the reply, my original post wasn't clear enough, but those are the manifold burner orifices, not the pilot flame orifice.
Sorry, your post was very clear; I missed the key word.
I don't think the pilot assembly is a Weil-McLain part; probably Honeywell and I don't know where to find the orifice size. And I don't think they sell the orifice by itself, but I've never looked for one so I may be wrong. You might have to buy the entire pilot assembly.
Two btu per sq ft for degree difference for a slab1 -
Thanks again. Yes, I've found an original, NOS, White Rodgers E50-104 Pilot burner electrode assembly on ebay, but they don't come with a new pilot orifice.
New Pilot orifices are available, but I want to make sure I purchase the correct one.
This page might help
WM used the WR cycle pilot on several of their gas boilers, the natural gas pilot orifice is pictured as #3 if you click on the screenshot you can zoom in. It has a .020" diameter orifice and that is a little larger than standard orifice for Honeywell, WR and other manufacturers. If you use the WM part number 560-528-958 at the supply house you can expect to pay triple. Just ask for the natural gas orifice that fits on the end of the 1/8" pilot tube. That should be all you need if your counter man has any experience.
This one may fit https://www.supplyhouse.com/Resideo-390686-5-020-Natural-Gas-Orifice
If that is not the correct shape than try this one https://www.supplyhouse.com/Robertshaw-10-208-022-Natural-Gas-Orifice-for-Robertshaw-1820-1830-Series it is only .002 diameter larger and should be fine
Those are the two different orifices that slide over the 1/8" pilot tube that I remember using.
Hi, Thanks for the reply. My Pilot Burner Electrode Assembly is E50-104, photos attached. It appears that the gas tube threads into the orifice. I found one which I believe could be the correct part, but I want to confirm the part number before I order it, attached here are two photos of what could be the correct orifice that I'm trying to confirm.
Pilot assembly
Weil McLain charges too much. and that WM part number does not have the electrode for the sparker. It is for standing pilot burner only. This one looks a lot like yours https://www.supplyhouse.com/Baso-Gas-Products-Y90AA-3223-1-4-Inlet-Fitting-w-023-Orifice-Natural-Gas. It has a .023 orifice
Will keep looking for .020
Here is a .021 orifice https://www.controlsincgas.com/Product-Name/Y90AA3221
Thanks! I am going to disassemble my pilot assembly to see if there is a size stamp or marking on it to confirm.
Why do you need one?
I'm installing a new Pilot assembly and would rather not reuse a 25 year old part if i can avoid it.
Measure the old one. It is just a piece of metal with a hole in it, it will last well over a century.
What you should be worried about is that the mercury flame switches are not quite obsolete but the new ones are super expensive and tend to be unreliable.
I found and bought an original NOS Pilot assembly on ebay , made by White Rodgers for Weil-McClain. It has the same part number as my original, with the spark ignitor lead installed, and it comes with a new pilot orifice as well so I'm good to go!!! The pilot orifice has 2090 stamped on it.
@Gary_24, I've merged your duplicate discussions into one here to prevent confusion.
Forum Moderator
1
- 50 Industry Classes