One zone heating - ghost flow
Hello I have one zone that heats up without a call for heat.
The taco relay isn’t calling for heat and the taco circ pump isn’t running.
I replaced the circulator pump assuming the check valve failed inside the unit. Taco 007 model, but my issue persists. Specifically on this one zone and not the others. It happens when my boiler is heating domestic hot water.
Any words of wisdom?
Times are tough and money is short so I’m reluctant to call someone out again to hit me with a huge bill.
Thank you!
would suspect a bad mixing valve …
Whats with all the mixing valves? 3 zones of radient?
It's hard to see the piping. At least 2 low temperature zones.
Those are IFC circulators pumping down?
You could try a compression spring check on a vertical return. Though it's more of a Band-aid than an actual fix.
what changed in the system, or has it always overheated in that one zone? The check valve holds up to approximately.5 psi for obvious reasons, the pump discharge pressure has to overcome IFC to satisfy the zone. You can replace IFC only without replacing entire pump. It’s an off the shelf item. It’s one of your other zone pump overcoming the IFC check if you’ve done a physical inspection and no system debris hindering the check from fully closing allow water to go through that zone whenever one of the other three zones energize.
If it persists, to mitigate you can install an external check valve on the return where most of delta p eroded through pressure drop in that zone, or go with a zone valve as a positive shutoff. That will permanently stop flow. Hopefully this helps. Taco has a technical support team at 401-942-8000. They’re very knowledgeable and can offer additional support
Joe Mattiello
Taco Comfort Solutions1 -
Is there a boiler curculator in the piping we font see? How us the indirect pioed?
ghost flow is is often the return piping, feel that to see if it warms first, or is warmer than the supply side. some systems need supply and return checks, usually primary secondary piping , however
You should always pump away from the mixed outlet of a 3 way thermostatic valve, pulling the blend of hot and cold. I can’t see those valves working properly piped like that?
Living the hydronic dream1
- 116 Geothermal
- 169 Indoor-Air Quality