Boiler Power On Without Programmer?
qupsklwv3kbd
qupsklwv3kbd Member Posts: 2
edited September 2024 in Strictly Steam
Good morning. I have a Baxi Megaflow Condensing (gas) boiler. It's about 10 years old.
Recently the boiler is not powering on. I checked the current to the boiler, it is receiving 240V AC (I am in the UK), so not problems with the wiring. I have disconnected the programmer but I am surprised the boiler does not power on without the programmer connected, even though it is receiving a full current. Is this normal? I am replacing the programmer as well (because it does not power on either), but I just wanted to check whether there is also a fault with the boiler as well. I would expect if you give it a power it should power on with/without the programmer connected.
Thanks for your opinion.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,345
    Check the low voltage transformer for voltage , it should be fused ….
    HVACNUT Member Posts: 7,197
    I'm not familiar with that particular boiler, but there must be a trouble shooting flow chart in the manual. If the service manual is seperate, you should be able to download it.
    You say the boiler doesn't power on without the "programmer" connected, but what do you expect to be powered without it? If all commands go though the programmer, what can be powered? Are you talking about external zone panels, or relays or something?
  • qupsklwv3kbd
    Thanks for the comments, the problem was a fuse on the boiler PCB. Didn't realise the same circuit from the mains AC goes through the programmer and boiler, so if there's no electric connection both boiler and programmer will not be powered.
    In the UK we call the timer a "programmer".
    PC7060