Ibc boiler
Options
plumbit
Member Posts: 20
I have a IBC boiler with a taco single zone controller. I had another zone roughed in and hooking up now. I have extra single zone taco controller can I wire it up to the boiler same was as the previous zone controller or do I need a 2 zone relay controller?
0
Comments
-
-
so just wire it same way as the original one?
not a problem having two thermostat wires going to the boiler terminals?0 -
Happens in effect w/ a single , 2,3, 4 or 6 zone relay. Its just a set of dry contacts.
0 -