viessmann 222 combi
Bill_44
Bill_44 Member Posts: 5
Getting an F3 (Combusion control) fault; resets @ "R". changed ionization & igniter. What else to check?
  • psb75
    psb75 Member Posts: 1,101
    Clean the heat exchanger. Check the condensate trap. Basic yearly maintenance.
  • GGross
    GGross Member Posts: 1,733
    F3 is a weird fault, flame is already detected at burner start, you need to check the flame sensor and cable. I would contact tech support for that one.
  • Derheatmeister
    Derheatmeister Member Posts: 1,659
    Static Gas pressure..Running Gas Pressure.Basic maintenace such as cleaning both rods.Make sure the polarity is correct including propper ground !