Oil direct vent
camiarrobino
Member Posts: 83
in Oil Heating
What enables an oil-fired furnace (or boiler) to be direct vented (as opposed to chimney or power vent)? I had thought that direct venting was generally only for high-efficiency condensing natural gas / propane burning machines?
Balanced flue with a Riello0
You can't just do it because you want to do it. Only on a positive pressure boiler. And your application must meet code and manufacturers specs.
And to be clear, you're not asking about a Power vent, right? Because that's a completely different animal.0 -
I wouldn't consider any type of sidewall venting on oil. If something goes wrong, the outside wall near the vent will get covered with soot. Given the typical "maintenance" we see on oil units, this is more likely to happen than not.All Steamed Up, Inc.
Consulting1