Can I control DHW and Pool loop with just the Munchkin boiler (no external control)
BVD202004
Member Posts: 2
I have an existing Munchkin boiler and wanted to know if I could control the DHW and Pool loop with just the boiler and no external controller. Both loops operate at 140 degrees. DHW loop takes priority over pool.
What temperature do you want the pool? That needs to be set into a control somewhere.Bob "hot rod" Rohr
it depends on how its pipe. if the domestic hot water is piped with a branch off the boiler loop you could. DHW sensor will go directly to the 925 control board. set point control lands on t-t on the 925. Eliminate the outdoor sensor so you can set the system temperature to 140 and don't have the warm weather shutdown shutting the pool loop.
This only works if this is the only two zones on the boiler. if you have more zones it will get more involved0 -
I have a circulator pump along with the DHW and Pool pump. I see landing spots for the CHW and DHW Pumps. Where would I tie in the pool pump?0