how do I measure overfire draft in Buderus 115ws3?
alias2102
Member Posts: 10
The boiler has a special port for this purpose. It is a brass nipple with a screw. Unscrewing it reveals a tiny pinhole. It is so small that no static tip fits through it. Another problem is boiler door insulation on the other side of the pinhole. I saw no hole on the other side of the boiler door when I opened it. Essentially, the pinhole is blocked.
How does one measure the overfire draft in Buderus?
It is in the instruction manual.
I usually just attach my probe to it with a piece of rubber tubing. A piece from my manometer or a piece of old pressure switch tubing will work.0
Perhaps, these 2 photos illustrate the problem better. First one shows the pinhole next to the static tip. Pinhole diameter is barely 1/16 in. The other photo shows the other side of the port. There is no opening into the chamber. There is a small hole next to the viewport but it is not connected to the pressure port.
I'm not sure how connecting a tube to the port with no opening into the chamber would help.
In my experience all the Buderus boilers I've worked on have a port that you loosen a small brass plug with a small flathead screwdriver. I unscrew the plug a bit and slip the hose over the port and attach my Testo probe or a manometer to measure the draft. What you have pictured looks different from what I usually encounter.
I would use one of those insulation support rods (commonly used as a search bit) in my cordless drill to make that opening communicate with the chamber, then attach one of these to the 1/8" or 1/4" female pipe thread
Then attach the rubber hose from the draft measuring device to the barb side of the fitting.
Or you could just open the glass sight door by removing it. You can certainly get a reading through the sight hole using the probe without removing the rubber tubing from it. Sometimes that boiler operates with a positive pressure, so wear heat resistant cloves like the fire fighters use.
Working on heating equipment, your tool box should have those gloves. Also I had 3 different barb fittings in my combustion analyzer kit. 1/8" 1/4" and 3/8" by the 1/4" tubing size of my manometer, or draft gauge.Edward Young Retired
I just can't believe Germans would design a pressure port in such an odd way. There must be some trick to it. I have a gnawing suspicion that the port hole connects via a lateral door passage to the much bigger sight hole. I need to test this theory.0
These Germans are a clever bunch. The pressure port does connect laterally to the sight hole (see the photo). It is angled. This design avoids measuring compounding effects of both static and velocity pressures when measured parallel to the flow.
The 115 is a three pass positive pressure boiler . You don't take measurements on the busness side . I believe that port is used on German controls , over there ...
Big Ed_4 said:The 115 is a three pass positive pressure boiler . You don't take measurements on the busness side . I believe that port is used on German controls , over there ...
When Buderus offered the G125BE in the States, you used a manometer at that port to check/set static pressure.0 -
I discovered that sticking a 1/8 " silicone tube into the port was a simple solution. It fits snuggly in the pressure port. It gave me +0.01 overfire, and the breach was at -0.02. The numbers comply with the Riello 40 F3 spec.0