Burner Won’t Kick on Below 66
Lildee1198
Lildee1198 Member Posts: 1
We moved into this house in July and figured out that the burner won’t kick on if the thermostat drops below 66 degrees. We changed the thermostat and it is still happening. It will turn on if we hit the reset button.
  • GGross
    GGross Member Posts: 1,902
    Unless the thermostat is a communicating device, the burner doesn't know what temp the thermostat is set to. More than likely the burner is locking out, and you are seeing a low thermostat temp as a symptom of the problem. To help you we need to know first and foremost what type of heating system you have, there are many burners in this world. We need to know, is this a boiler or furnace? what type of fuel? model of the boiler/furnace, if it is an external burner what model is the burner? what thermostat do you have?
  • Big Ed_4
    Big Ed_4 Member Posts: 3,530
    What reset button ?
  • neilc
    neilc Member Posts: 3,183
    thermostat set (incorrectly) for heat pump, and locking out W1 at too high (incorrect) setting 66* ?????????
    what boiler furnace or heating system is this?
    what thermostat is this?
    pictures of both
    and yeah, what reset button?
    known to beat dead horses
    HVACNUT Member Posts: 7,450
    Hitting the reset button on the burner means there's a safety issue with the burner.
    If you're not familiar with oil, it needs to be serviced, or at least combustion tested annually. Ask around. Get reviews in your area for reputable oil service companies, and call. Because it's not DIY. Where are you located?
    And repeatedly hitting the reset button usually doesn't turn out good for anyone.