Draft Control flap slams when Buderus oil boiler shuts off
cckriss
cckriss Member Posts: 38
https://streamable.com/byhl4r
Here is a video of what happens.
The Buderus boiler was installed a few years ago, this never happened. A couple of months ago, i had the exhaust liner replaced.
What is happening? It’s so loud.
    HVACNUT Member Posts: 6,843
    What size liner was installed?
    What model Buderus? The G115 has a 5 inch flue while the G215 uses 6 inch.
    It's not abnormal for the regulator to move when the burner shuts off, but I don't see it budge during the run. A draft test must be done, and the regulator adjusted. With either the G115 or G215, Buderus specs 0 to slightly positive draft over fire, and -.02 breach. Smoke and combustion tests should be done as well. Has it been serviced since the installation?
    Big Ed_4
  • cckriss
    It is G115 with 5”. Before the liner, it was -.05 as measured by the boiler installers. An energy auditor measured it at -.01 and said it was not enough and i should call a chimney company. The chimney company said the original flue tiles had alot of yellow deposits and it should be re-lined. I dont know what they measured.
    I used to occasionally smell very very slight diesel fumes near the boiler when it first starts up. After re-lining, i no longer smell anything.
    The boiler has been serviced once, before re-lining.
    Have it tested again. Combustion, smoke, draft.
    EBEBRATT-Ed Member Posts: 18,185
    When the burner shuts off the flame collapses and causes the draft to change instantly. This is common. If the burner does not have a post purge perhaps that can be added it would quiet the shutdown
  • cckriss
    Is this something I can DIY? If not, do I call a plumber? HVAC guy? Chimney guy?
    Thanks
    cckriss said:
    Is this something I can DIY? If not, do I call a plumber? HVAC guy? Chimney guy? Thanks
    You call an oil burner tech.
    What burner? A Beckett or Carlin needs to have a primary capable of post purge. If it's a Riello, it needs a post purge timer module.
  • cckriss
    edited April 2024
    It's a Buderus G115. Oh I believe it's a Reillo 40.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,233
    edited April 2024
    Sounds correct to me with your Buderus and a perfect sized liner ..
  • cckriss
    It's really loud. I can hear it from the 2nd floor.
  • Big Ed_4
    Your Buderus can be fired direct vent . It serves no purpose on your boiler but it is code... A missed placed screw could lock it in ....
    GrallertEdTheHeaterManSuperTech
    What serves no purpose, the draft regulator? If draft is greater than -.02 at the breech, how do you "regulate" that?
    And direct venting would require a balanced flue with the BF Riello, not the F3 or F5 40 Series.
    EdTheHeaterManDJD775SuperTech
  • Big Ed_4
    edited April 2024
    You are right , ...The banging of the damper , the static pressure is high or location on damper