Radiant floor setpoint
zepfan
Member Posts: 444
We have a job that has in floor radiant heat system, and fan coil units. There are separate pumps for the fan coils and for the radiant floor. The building has a condensing boiler, so we can run a very low return water temperature without damaging the boiler. The boiler has the option for three different priorities, Currently the fan coils have a setpoint of 180 degrees, and my question is what should the setpoint be for the radiant system? 90 degrees? It is a concrete floor, with four different zones. We do not have a lot of radiant systems here.
Thanks to all
Thanks to all
I had a radiant heat in the Concrete Slab Addition system in my previous home, I also used a condensing boiler. I got plenty of heat using a 110°F water temperature with a 10°∆T so the average water temperature was about 105°F. The remainder of the home was a staple up using aluminum transfer plates. That 110° water was about the highest I wanted to put on those Hardwood Floors.
If you do not have Hardwood floors to worry about, then I would start at 120° and go down from there. If you get the temperature to over run the thermostat setting by more that 3°F then lower the boiler temperature by 5° and see how that works for a few days. You need to let it operate for at least 3 days before you try another temperature change. It can take that long for the Slab to change temperature and see if it is any better.
It may take 24 hours for the 120° boiler water temperature to show up as a room temperature change when you have a large mass like a concrete slab.Edward Young Retired
you might run the unit heaters lower also. The lower the swt the more efficiency you get from the boilerBob "hot rod" Rohr
Living the hydronic dream0