Boiler turns off after a few minutes
Tom78
Member Posts: 6
Hi all. I need some help if possible. I have an old American Standard GPH boiler. Earlier this fall I replaced my relay and the aquastat. Now it runs at most 3 minutes and shuts off the burners and pilot light. I’m not sure why it’s doing this. Could I have miswired it? The pump runs no issues. It’s all one zone.
The aquastat is a Honeywell TA418A1023 new, old stock and the relay is a Resideo RA832A, I replaced that because I’d have to slap it every couple of days last spring to make it work. I’ve also replaced the thermostat a Honeywell CT87K, with the same unit, just new.
I’ve included pictures of all of them. Thanks for any help you can give. I’m hesitant to call a tech out because I don’t want them to say I have to replace it, I know that I just can’t afford to for another season at which point I plan on buying a mini-split system.
What was the old aquastat set at? It looks like you have the new one set at 110 degrees with a differential of about 10 degrees which is far too low for a conventional cast iron boiler.
You should really get a good tech to look at this. A competent tech won't tell you to replace it unless it is leaking or you have a combustion or venting issue that can't be fixed. Finding a competent tech can be difficult.0 -
The aquastat is set the same as the one I pulled off of the boiler was. I just adjusted it to match what that one had on it. I've never played with any of the dials. Could that be what the problem is?0
I'll check that to make sure. I thought I did, no harm in trying it again.EBEBRATT-Ed said:Make sure the sensing bulb is pushed into the well as far as it will go.
Its for hot water heat, it has 12 big cast iron radiators it supplies. As far as what that aquastat controls I don't know and I don't know what controls the high limit. It always shuts off right around 22-25 PSI and 180-190.109A_5 said:Hello @Tom78,
What is this boiler used for ? DHW only, Hot water heat, Both ? The aquastat pictured seems like it would be for the low limit, what controls the high limit ?0 -
Hello @Tom78,
Maybe more pictures of the whole overall boiler system and all controls would help.
I would think in that temperature range the aquastat would keep the boiler warm for DHW, which seems like you don't use that feature of the boiler system.
One Pipe System0