Multiple Issues
JDFUF
JDFUF Member Posts: 4
Peerless boiler - block was rebuilt in 2021. Boiler serviced end of October 2023 before the system was turned on for the season. Water level is currently overfilled
Banging on pipes in incessant
valves have been changed
Oh - and there is an entire wing of the house that the heat doesn’t reach.
    mattmia2 Member Posts: 13,469
    What happens if you drain it down to the proper level?
    JDFUF
    EdTheHeaterMan Member Posts: 10,766
    edited January 2024
    Copper near boiler piping may be the incorrect size. You will need to remove the insulation on the copper pipes only, and take more pictures. The original installer was not a Steam Boiler Installer, otherwise that copper pipe would actually be Steel pipe with iron fittings.
    The fact that you mentioned overfilling leads to another problem
    JDFUF
  • JDFUF
    @mattmia2 I’ve got to figure that one out
  • JDFUF
    @EdTheHeaterMan any idea what the correct steel pipe size would be?
  • JDFUF
    The size will come from the near boiler piping diagram in the manual for the boiler. If it is plumbed in copper there are almost certainly other things that are incorrect about the piping.
    not sure if this is your boiler, but it looks close:
    edited January 2024
    I tried to look for an article or video where @DanHolohan explained what happens to steam mains that are hanging in a basement ceiling or crawlspace when they are filed with water. The steam pipes are installed to insure that condensation does not get trapped anywhere. The pipes are installed to a minimum slope based on the design, One pipe counter flow, One pipe where the condensation and steam flow in the same direction and different two pipe systems. This pitch or slope is important and sometimes when a home settles over decades that slope can become out of wack.
    Now consider this, the most weight those pipe hangers are designed to hold are empty pipes, with no water in them. Only air or steam (which is lighter than air) are supposed to be in those pipes. Now you add the weight of water to those large 2 or 3 inch mains and watch those 50+ year old hangers give a little. It is quite possible that your entire system of steam mains are now out of wack and there are several low spots that are trapping condensation (water) where it should not be. That can cause some serious banging.
    Do you own a level? One of those 6 foot ones. And perhaps a 2 ft one for the shorter pipes and maybe even a 6" one for between those really short pipes. Everything must be properly pitched to get the water to flow back to the return pipe to the boiler.
    LRCCBJ
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,643
    You said it well, Ed.
    Retired and loving it.
  • EzzyT
    EzzyT Member Posts: 1,368
    I would start with correcting the near boiler piping and then go from there.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Grallert
    Grallert Member Posts: 969
    Bring the water level down to operating level in the glass. That's a good place to start.
