whats your experience with brazed plate heat exchanger running small water loop off a steam boiler?
Joseph_4
Member Posts: 320
GM all. Im putting in a steam boiler for a customer and curious to know whats your experience with a brazed plate heat exchanger running water loop off a steam boiler?.. Id be running 15k loop on this job.. I've used Everhot before but the smallest one is 4x cost of brazed plate. ive been told they get plugged up. customer plans to knock down house in 2 to 3 years, would rather not spend a lot . i want to do a a heat exchanger specifically
I'd appreciate any pointers. (ive installed brazed heat exchanger before but never with steam)
thx
Joe
thx
Joe
If the house is coming down in 2 or 3 years and the owner is hell bent on putting money into a landfill, I'd say skip the heat exchanger entirely and run the boiler water right through whatever emitter you are installing and call it a day. I'd even say run a cast iron circulator, it should last long enough.
On a side note, it strikes me as quite odd to put any money into something I'm planning on tearing down.1 -
I would install it like an Everhot. I would put a strainer on the inlet water steam side. Are you doing the inlet side gravaty or pumped? Regardless you need a circulator, expansion tank amd water MU on the HW side.
There is a method of using boiler water which would be less $$. Piping has to be tight with no vents if you go up above the boiler water line.0 -
I've tried all ways.. Everhot, Nothing, Flat Plate. I prefer Flat Plate HX. .but....
I set them up with brass unions, drains tees and valves and a Brass strainer upstream. As long as you flush out annually...never an issue..they are so tiny and cute! Mad Dog 🐕0 -
Nightmare. Constantly plugging up. Used to think it was a good idea until you put it to work. not enough space in the HX. prefer TFI/everhot0
Would I put one on an ancient system with buried, clogged, steel returns??? NEVER!
If you have Muddy splunck that thick in your boiler and returns, the maintenance is lacking severely, so don't bother. That being said, and I've used Many Everhots, is the compact size of a Flat Plate HX is a HUGE advantage in these ever shrinking boiler and mechanical rooms. Their footprint is not as issue. I WILL find this picture...today..
1) With brass unions on each of the 4 ports, removal and flushing is a 15 minute job. 2) If your returns are not clogged & nasty, a Brass wye Strainer on the Boiler inlet catches any other splunck. 3) To make it even easier, I put brass tees & boiler drains
On each port with isolation valves for easy flushing with Street Water Pressure. I have close to 100 out there some installed 20 years ago...never an issue...even with out yearly flushing. My Two cents Mad Dog 🐕0 -
thanks for all feedback.. appreciate it..appreciate hearing the experience.. would love picture Mad Dog0
I'll track one down recovery from Nasty flu. Stay Tuned. Mad Dog 🐕0
Ok, found it. This is about 8 years imstalled. Clean the Wye strainer once a year ...done! Hasn't clogged yet. MAD dog 🐕
I just changed out a wall tstat for BB heaters that were installed 35+ years ago.
Just to point out trouble free operation.0 -
K Copp..Happy New Year! .As I said, NO steam system should be that neglected that the splunck is that thick and purulent. Take the Flat Plate HX out of the equation. The system either has old buried wet returns sans purge tees and valves or was just Never flushed regularly. In either case, the way I pipe FPHX I pipe them, anyone that can shut a valve and open a boiler drain and screw on a hose, can flush them very easily.
Even if they get lazy, Crack the 4 brass unions nuts and put the whole thing in a sink of hot water and white vinegar for an hour, and hook up an air compressor or just 50 psi of Street water pressure. Like new. Mad Dog 🐕0 -
Agreed.Mad Dog_2 said:K Copp..Happy New Year! .As I said, NO steam system should be that neglected that the splunck is that thick and purulent. Take the Flat Plate HX out of the equation. The system either has old buried wet returns sans purge tees and valves or was just Never flushed regularly. In either case, the way I pipe FPHX I pipe them, anyone that can shut a valve and open a boiler drain and screw on a hose, can flush them very easily.
No buried return on this one... its just steam. I deal with it and they pay me. No worries.