Help diagnose radiator noise
holograham
Member Posts: 118
I am a bit stumped here.
Happening on 2nd floor American Radiator Co. Peerless two column- 23inches tall, 22 sections, 51.33 EDR. Pitched correctly. In a radiator cover box. New Gorton 4 vent (room gets hot so venting slow) which replaced a decrepit ventrite (made same noise with ventrite). Noise happening at end of boiler cycle (so pressure is building before pressuretrol cuts off). Typically doesn’t happen on the short cycles (usually have 2-3 pressure cycles after the initial 40 min cold start).
Would say it’s pressure or wet steam related but why the only radiator making this noise?
Water is backing up in the rad. That causes the gurgling we hear. I bet the shutoff valve disc has broken off the stem, which blocks the returning water.All Steamed Up, Inc.
Consulting1 -
Other than the noise - is this urgent to fix? I forgot about the broken valve disc potential.Steamhead said:Water is backing up in the rad. That causes the gurgling we hear. I bet the shutoff valve disc has broken off the stem, which blocks the returning water.
Not life-threatening, but it could make the vent spit and of course the noise is quite annoying.All Steamed Up, Inc.
Consulting1 -
Ok thanks - yes vent is spitting and is brand new. You can hear it at the end of the video.0
