To ECM or Not ECM
CurtT
Member Posts: 7
Single zone at this time through fan coil with provisions on the secondary loop for additional emitter zones with Zone Valves. Single Grundfos circulator (3 spd) very little head loss at this time and no more than 5 gpm. Should I spend the money to upgrade to an ECM while on single zone, or wait, or maybe don't do it at all? I like the idea of the pump helping decide gpm more accurately that Low, Med, or High.... My inclination is to wait until system is built out to 2 more zones on valves.....
It really comes down to your electric rates along with flow requirements of each zone. I was all about ECM for several years until I started having trouble with them. At this point, the payback in most residential systems (with my local power rate which is lower than most) is upward of 20 years and I don't foresee many of them lasting that long. I've gone back to the good old 15-58 variety of circs on the majority of systems, but I do use the Alpha 26-99 on occasion for higher demand systems.3
Somewhat off topic:
I use the Alpha I 15-58 when there are multiple zones, but recently needed to pump 10 GPM at 10' of head and the Alpha I was not strong enough. The Alpha II 26-99 is way too strong and there is nothing in between. Ended up using the larger pump anyway as Taco pumps aren't convenient from my regular suppliers. I left the differential pressure relief valve in place.
Note to Grundfos: Give me a nice user interface screen on the Alpha II like you have on the Alpha I.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1
