System 2000 issue--one zone always open
Try removing the wires at the zone valve itself. If it is a spring return type valve, you should hear is wind close.
Honeywell, Erie, Caleffi are examples of spring return valves.
A pic of the valve could help troubleshootBob "hot rod" Rohr
Hello @stlblufan,
Which manager do you have ? There may be some diagnostics for it.
https://energykinetics.com/control-diagnostics/
One Pipe System0 -
Perfect diagnostic suggestions, @hot_rod and @109A_5 . @stlblufan , let us know what you find.If the zone valve is bypassing without the wires connected, then the zone valve will likely need to be replaced.
If the T3 output is damaged and you have an open fourth zone, you can move the zone 3 thermostat and zone valve wires from T3 and Z3 to their respective connections on T4 and Z4.
RogerPresident
Energy Kinetics, Inc.0 -
Thank you all. I have the Digital Energy Manager. Pictures of the manager and the zone valve attached. FWIW I tried disconnecting both T3 and Z3 and that resulted in just the Power light being on when I turned the system back on. I think that's what is supposed to happen but I don't know what that means in terms of what's at fault.
One Pipe System0 -
This is with T3 removed. The problem here is that T2 is calling but not showing up.
EDIT: actually T2 went into Eco mode when I turned off the system so it wasn’t calling.
EDIT2: just to be clear, the thermostat for this zone is set at 40F. I've also tried taking the thermostat off the wall, but the T3 call still lives on and the zone remains open. The wires do not appear to be shorted on either end, but I guess I can't rule out something in between.
Hello @stlblufan,
Is you system wires like the diagram below ? I don't see anything stuck on in your last picture.
Anyways, I would swap the T3 (the original zone 3 problem) with T1 (a correctly working zone) and also Z3 and Z1 wires at the Energy Manager terminals. See if the problem follows the Energy Manager or the external wires.
One Pipe System0 -
Might not be a wiring control problem.
@stlblufan
Do you have a flow-control valve on that zone? It sounds like that is the problem.0 -
@stlblufan , the only way the thermostat light can come on is by completing the circuit, which happens through the thermostat and wiring. @HVACNUT , thank you for your post, you nailed the diagnostic! Faulty thermostat, short in thermostat wiring, or T2 and T3 are switched...
RogerPresident
Energy Kinetics, Inc.2 -
Thanks guys. I don't think it can be a faulty stat because removing the tsat from the wall doesn't result in any change to the system. I also do not think it could be a switch of T2 and T3 because this issue just started spontaneously a couple of days ago. So it sounds like a short, which will be super fun to track down. Thanks again for everyone's help.0
Is there only 2 wires? Hopefully there's other wires you can use.stlblufan said:Thanks guys. I don't think it can be a faulty stat because removing the tsat from the wall doesn't result in any change to the system. I also do not think it could be a switch of T2 and T3 because this issue just started spontaneously a couple of days ago. So it sounds like a short, which will be super fun to track down. Thanks again for everyone's help.
Anyone hang a picture or shelf or something recently? Got vermin?0 -
Vermin could be it sadly. Rural VT.0
Hello @stlblufan,
OK as long as you moved T3 and Z3 as a set and the problem followed the wiring the Energy Manager is probably not at fault.
The "Buffer End Switch" has me curious. Is there other equipment in-between the thermostat and the Energy Manager ?
If not inspect the wiring closely between the thermostat and the Energy Manager. It maybe chafed or crushed somewhere, like under a staple that has pierced the insulation of both wires going to the thermostat. A multi-meter with an audible continuity test function may help too.
One Pipe System0
- 87.2K THE MAIN WALL
- 118 Chimneys & Flues
- 113 Geothermal
- 164 Indoor-Air Quality
- 73 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam