not getting enough hot water from tankless coil
mortyb
Member Posts: 2
When we moved into our house 8 years ago, we got great hot water for showers and baths from our Peerless WBV-03 boiler with tankless coil. Then after about 2-3 years it got much worse, temperature was fluctuating and unable to keep up for showers and even worse for baths. First we cleaned the coil, then we replaced it, but we never got back to the way it was when we moved in. Any thoughts on what might be going on? We have well water and scale has been a problem.
We have a L8124 Honeywell Triple Aquastat. The settings seem odd based on reading through other posts. HI is set to 195, LO is set to about 197, DIFF is set to 12.5.
I'm tempted to either remove the tankless and put in a Superstor indirect, although I'm not sure if this boiler will run the Superstor. Or put in an electric water heater in series with the tankless.
Any input would be appreciated.
Thank you!
Thank you!
1.) Get a 65 gal. or an 80 gal heat pump water heater. Brad White, Rheem, or State/A.O. Smith. Not much sense in connecting it to a failing coil in the boiler.
2.) Get an indirect tank and put a priorty zone on your boiler.0 -
The starting point for your L8124 aquastat should be 180°F high, 160°F low and 10°F Diff. If that does not get you where you want to be, then increase both the high and the low by 5°F Wait a few days before increasing the temperatures.
When you replaced the Coil, Did you install a thermostatic mixing valve? That can help with overheating and temperature fluctuation that is always a problem with tankless coil water heaters. If you do not have a mixing valve, you will always have fluctuating temperatures based on the operation of the burner nad circulator pump during heating and non heating cycles.
Here are 3 different boiler manufacturers instruction diagrams on tankless coil installation:
This is the one I used when installing or repairing Tankless coil jobs: https://www.supplyhouse.com/Resideo-Braukmann-AM100-US-1LF-1-2-Lead-Free-Union-Sweat-Mixing-Valve-70-145F?_br_psugg_q=am100-us-1lf
1
- 116 Geothermal
- 169 Indoor-Air Quality